Hello.
So I've learned a lot about dimmers on this last job. The customer wanted everything downstairs on dimmers and boy has it been a learning curve.
I've split a lighting circuit and the customer has asked for 2 x st64 led bulbs on pendants to be put on a dimmer. The problem is they're flickering on some settings of the dimmer.
They're pulling about 10w
And the dimmer is rated at 60-400va which I believe kind of translates to 60-400w (but not true power)
So I think the issue is because they are below the minimum required load for the dimmer.
The bulbs are dimmable.
Does anyone know if you can get dimmers rated lower than the one I have list above.
Or will I need to put them on a dimmable led drive?