Hello.
So I've learned a lot about dimmers on this last job. The customer wanted everything downstairs on dimmers and boy has it been a learning curve.
I've split a lighting circuit and the customer has asked for 2 x st64 led bulbs on pendants to be put on a dimmer. The problem is they're flickering on some settings of the dimmer.
They're pulling about 10w
And the dimmer is rated at 60-400va which I believe kind of translates to 60-400w (but not true power)
So I think the issue is because they are below the minimum required load for the dimmer.
The bulbs are dimmable.
Does anyone know if you can get dimmers rated lower than the one I have list above.
Or will I need to put them on a dimmable led drive?
 
Varilight is what I use, although Kew Electrical do one not sure brand that works too, but similar price, an alternative option that I've recently discovered, all screwfix dimmers appear to be compatible with dimmable led lamps,
 
Always check on the dimmer manf. website to see what lamps/fittings/drivers it has been tested with otherwise it's pot luck and even intermittent faults can occur for no logical reason. Oscilloscope on circuit All becomes clear.​
 
Guys thank you all for your help.
I went with the majority and used varilight v pro's and I think it's safe to say I won't be using any other dimmer modules in future. They're the dogs nuts.
I had a callout back to the job because one of the aroura2 dimmers started buzzing so I've swapped that over too. And they're super silent.
 

Reply to LED lights from dimmer flickering. Load is below dimmers minimum rating. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have purchased spotlights as below, but they are flickering when I dimmed them down to around 15-20%. We have installed 8 x ALUSSO LED Recessed...
Replies
4
Views
1K
I have the typical LED on Dimmer switch. All the lights flicker in my house are very inconsistent times. By let me clarify by saying all the...
Replies
0
Views
911
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
708
I've read lots of conflicting information on the internet about dimmable LED lightbulbs. Some people have said that even if a supplier claims that...
Replies
2
Views
2K
Per this document: https://www.lutron.com/TechnicalDocumentLibrary/048487.pdf I guess dimmer switches have a minimum load required for operation...
Replies
2
Views
591

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock