Hi Guys, we are currently trying to locate several SWA cables in and around our carparks. I have bought a Fluke 2042 cable Generator and Locator but am struggling a bit.

The Gen has 2 ports on the top, can anyone advise on where we connect these to the exposed (dead) SWA? We think there may be a break in the cable so currently getting a >500 with our 1652 on insulation resistance. Does the cable need to be complete (joined at one end) to work or can we do it as is?

Also the generator has 3 strengths, any idea which is best?

Thanks again.

Also on a second note (Apologies it has been a few years since I finished college), when performing a IR test on the cables, at 250v it gives us >200 straight away. But when at 500v is starts off around >120 and slowly climbs to >500, why is this (Fluke 1652C)

Kind regards
 
Connect the + terminal to a core of the non powered cable (or the armour) and set the transmission level to high if the cable is properly buried.

Use the receiver at the start of the circuit and select the sensitivity somewhat higher than that required to detect the accessible cable, as you move away you should be able to trace the cable location, if there is a break in the core you are connected to then the signal should be lost at that point. Then try again from the other end and if the point of signal loss matches there is the break.
 

Reply to Locating with a Fluke 2042 in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
487
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
4K
When putting in some duct for fibre broadband we also put in a few lengths of 63/50mm twinwall duct "just in case" we needed that, as we knew of a...
Replies
9
Views
1K
For emergency use, when there's a power outage, the current situation (no pun intended) is that I'm running a hook up cable from the 16A socket on...
Replies
3
Views
2K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock