Discuss Maintaining top entry fire rating/IP rating in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
20
Evening all

Had a job yesterday, which I'm back at next week. Job was to install new dual tarriff CU. As can see from photo earthing was supplied off a clamp from incoming metallic pipe which contained the supply cables. As this old CU is double packed out with a frame it had ample space to house this pipe. Problem being when fitting new CU this isn't case. So after chat with mr NIC man I opted to drop board by 100mm jigsaw out top entry and use 100mm plastic trunking across top to house these cables and pipe. He seemed bit unsure at first as much as me but checked it out and said that as we have maintained IP4x at top all is fine. I questioned about the fire rating and he said that this is fine to. What are people's thoughts? I'm back there next week so maybe can improve but thoughts are even if use loads of glands on top and trunking on top surely these are only so resistant to spread of fire.
Cheers
20210301_112702.jpg
 
Last edited by a moderator:
What you're describing as a 'metallic pipe' looks very much like a two core 10mm or 16mm MICC or 'Pyro' supply cable. So using a pipe earth strap is a right bodge. Ideally this needs a proper gland and to achieve this it would need the existing pot removing to fit the correct gland, along with specialist tools.
Is the CU a long way from the meter ?
 
What you're describing as a 'metallic pipe' looks very much like a two core 10mm or 16mm MICC or 'Pyro' supply cable. So using a pipe earth strap is a right bodge. Ideally this needs a proper gland and to achieve this it would need the existing pot removing to fit the correct gland, along with specialist tools.
Is the CU a long way from the meter ?
The whole complex is done like this Dave there's about 200 properties. I'm not entirely sure what the proper name for it is but if you look at the photo the pipe comes in and has some sort of orange outer sheath then what looks like copper pipe is exposed and earth clamp is clamped to this. The pipe itself has 4 cores in it all black. 2 for neutral 2 for live with a wax substance around them. Yes the meters are located all the way down on the ground floor
 
Evening all

Had a job yesterday, which I'm back at next week. Job was to install new dual tarriff CU. As can see from photo earthing was supplied off a clamp from incoming metallic pipe which contained the supply cables. As this old CU is double packed out with a frame it had ample space to house this pipe. Problem being when fitting new CU this isn't case. So after chat with mr NIC man I opted to drop board by 100mm jigsaw out top entry and use 100mm plastic trunking across top to house these cables and pipe. He seemed bit unsure at first as much as me but checked it out and said that as we have maintained IP4x at top all is fine. I questioned about the fire rating and he said that this is fine to. What are people's thoughts? I'm back there next week so maybe can improve but thoughts are even if use loads of glands on top and trunking on top surely these are only so resistant to spread of fire.
Cheers
The copper pipe you mention is in fact an MICC (pyro) it needs to be glanded properly to your metal consumer unit to achieve a suitable earth. I would imagine that the main service head (cut out) is a fair distance away and not local. Are you working in a block of flats or a big communal building built 40,50 years ago where pyro was used frequently.
 
The whole complex is done like this Dave there's about 200 properties. I'm not entirely sure what the proper name for it is but if you look at the photo the pipe comes in and has some sort of orange outer sheath then what looks like copper pipe is exposed and earth clamp is clamped to this. The pipe itself has 4 cores in it all black. 2 for neutral 2 for live with a wax substance around them. Yes the meters are located all the way down on the ground floor
Replied same time as me answered my question ?
 
Yes it's the cable I described Mick 2 cores for the 24 hour supply and the other 2 for off peak presumably. If changing the board I can't see any other correct option other than glanding it properly. If you don't have the experience or tools to do this [and not many have these days to be honest], you might need to ask around and find someone to give you a hand with that part of the job.[Assuming you can still source the right gland] Unless anyone else can suggest another compliant way of connecting the copper sheath to a sizeable earth conductor.
 
Yes it's the cable I described Mick 2 cores for the 24 hour supply and the other 2 for off peak presumably. If changing the board I can't see any other correct option other than glanding it properly. If you don't have the experience or tools to do this [and not many have these days to be honest], you might need to ask around and find someone to give you a hand with that part of the job. Unless anyone else can suggest another compliant way of connecting the copper sheath to a sizeable earth conductor.
Is a nightmare these supplies as a way of caution ive run a seperate 16mm earth to each flat on my previous jobs and ensured the pyro cable is glanded correctly to achieve suitable earthing. The responses I got a few years ago made me run seperate earth whilst upgrading kitchens and consumer units
 
Replied same time as me answered my question ?

Yes it's the cable I described Mick 2 cores for the 24 hour supply and the other 2 for off peak presumably. If changing the board I can't see any other correct option other than glanding it properly. If you don't have the experience or tools to do this [and not many have these days to be honest], you might need to ask around and find someone to give you a hand with that part of the job.[Assuming you can still source the right gland] Unless anyone else can suggest another compliant way of connecting the copper sheath to a sizeable earth conductor.
Thanks chaps. The thing is these apartments were built maybe 80's and all the properties I've worked on in there are done the same way and none are glanded correctly. Don't seem like many sparks nowadays can chuck their hand to this (including me) and don't know what chances are of getting the right glands? Loads of these properties are failing EICR's because no RCD's and not much way getting round this without CU change
 
I'm not entirely sure what the proper name for it is but if you look at the photo the pipe comes in and has some sort of orange outer sheath then what looks like copper pipe is exposed and earth clamp is clamped to this. The pipe itself has 4 cores in it all black. 2 for neutral 2 for live with a wax substance around them.
Even if you don't have the tools or skills, surely you can recognise an MICC cable??!!
 

Reply to Maintaining top entry fire rating/IP rating in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
929
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
741
Hi all So had some issues lately related to high current fittings .. dp switches mostly. A number of electric boilers of various ratings .. from...
Replies
24
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
519
So I had a ceiling repair done in my bathroom due to water damage. The neighbors toilet above me was leaking for who knows how long. Mold...
Replies
1
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock