Discuss Max run for 10.5 kw shower cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
16
If 10.5 kw shower installed on 10mm t/e and 45a MCB over 15m, is it likely to have any problem as shower leaflet states max 12m run? Cable clipped direct with the exception of 2.5m running through some pipe boxing (containing hot water pipe)
 
that max. 12m may refer to 6mm. can't see a problem with 10mm. have you calculated the VD?
 
This would be the area of most concern with me. How close are the pipe and the cable ? is the pipe lagged ? what's the ambient temp of the area ? etc
 

Reply to Max run for 10.5 kw shower cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
424
Hi, Same project as detailed in my other post (I want to run shower cables to the CU whilst the kitchen ceiling is disturbed). I'm going to...
Replies
5
Views
3K
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
551
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
444

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock