Discuss MICC Cable - phase to earth fault in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hello Gents,
I have a low IR reading on a lighting circuit - the circuit is 50 years old - i believe the fault is at the pot connection as there has been a downpour of water on this connection - I was going strip back the sheath and identify the point where the IR reading high - I was looking to connect the cable to an adaptable box , and then connect the outgoing from the box with FP 200 - Problem is I am struggling obtain an imperial pot to gland off at box - is there anything on the market that will enable me to connect the MICC cable into an adaptable box which will 1) maintain my earth continuity and 2) prevent any further moisture ingress in the existing healthy cable.

Thanks

Sparky 63
 
Hello Gents,
I have a low IR reading on a lighting circuit - the circuit is 50 years old - i believe the fault is at the pot connection as there has been a downpour of water on this connection - I was going strip back the sheath and identify the point where the IR reading high - I was looking to connect the cable to an adaptable box , and then connect the outgoing from the box with FP 200 - Problem is I am struggling obtain an imperial pot to gland off at box - is there anything on the market that will enable me to connect the MICC cable into an adaptable box which will 1) maintain my earth continuity and 2) prevent any further moisture ingress in the existing healthy cable.

Thanks

Sparky 63
If this circuit is 50 years old I doubt very much that this will be the cause if it was well made off at the installation date unless someone without proper knowledge has been buggering about with it.
As has been suggested, get a heat gun on it.
 
and tell us the IR reading that you consider low.
 
The really old smaller size cables I have come across quite often are difficult to work with , as they are very small and if buried in the wall have been prone to corrosive reaction with the cement and plaster , so I would be careful with them ,,,,
 
be fair. he might have needed to go to the offy for beer. :26:
 
First you do as said in previous posts, if this doesn't help, then get the size of the cable by looking on the pot for a number, see if there is a compatible size in metric, or source a pot that fits.
If you are unsuccessful then as the end is no good cut it off. Now the tricky part. Carefully dismantle the pot assembly, cleaning all parts carefully, make sure you get the three indentations out where the disc sits you can then re-use the pot and use new compound and a new disc. You should have a good termination It can be done, I have had to do it.
 
First you do as said in previous posts, if this doesn't help, then get the size of the cable by looking on the pot for a number, see if there is a compatible size in metric, or source a pot that fits.
If you are unsuccessful then as the end is no good cut it off. Now the tricky part. Carefully dismantle the pot assembly, cleaning all parts carefully, make sure you get the three indentations out where the disc sits you can then re-use the pot and use new compound and a new disc. You should have a good termination It can be done, I have had to do it.
I've never had to do it, how did you handle the olive mate?
 
heatr gun first option. one of those you strip paint with, but don't overheat the pot. the compound will disintegrate. another option is to hit it with 1000V P-E. leave tester on a bit and see if the reading increases.
 
I've never had to do it, how did you handle the olive mate?

Cut the pyro as near to the olive as you can at one end, using pliers work the remaining bit of pyro out, use a small file to open the ends of the olive, you will still have enough on it to grip the newly made termination. At least mine did, and it got me out of a hole (not literally)
 
Try unsealing the pot, not taking off,just the fiber disc, sleeking and get as much of the compound out as you can, in other words expose the end to the atmosphere and try, as someone else said a heat gun or a low flame torch, I had this many moons ago and it worked perfectly,
 
ok cheers and what if this doesnt work is there any way i can make any MICC into box without a pot connection - is there any new technology that can overcome this problem - i guess im looking for a quick fix -)
cheers
 
ok cheers and what if this doesnt work is there any way i can make any MICC into box without a pot connection - is there any new technology that can overcome this problem - i guess im looking for a quick fix -)
cheers
No sorry, not if you're looking for it to last another 50 years
 
What you could do is to get an alert box from a fire alarm, strip the whole thing down and remake the pot on the end of it but this will only work if the pot has the earth link on it (forget the proer name for it but it's a bare earth wire soldered in to the pot) if it doesn't have this you'll have no earth continuity
 
ok cheers and what if this doesnt work is there any way i can make any MICC into box without a pot connection - is there any new technology that can overcome this problem - i guess im looking for a quick fix -)
cheers

There are no quick fixes for MICC cable, and there has never been a method of taking a MICC cable into a box without either the sheath or the pot being clamped. I'm getting a distinct impression you are somewhat outside of your comfort Zone working with MICC cable. If so, i suggest getting someone in, that's happy and confident to undertake such repair work to MICC cable...
 
From the symptoms if only L is low I would suspect the pot, damp in the insulation will show all IR readings down.

Out of interest, what’s wrong with 300KΏ. Leakage = 0.7mA.
I certainly wouldn’t loose any sleep over it.

I don’t know where this 1MΏ minimum came from. I suppose it’s a quick fix for the modern electrician. When dealing with old installations you have to take a pragmatic approach.
I was brought up to calculate the maximum permissible leakage current as 1/10,000[SUP]th[/SUP] of the circuit OCPD or in the case of a motor the FLC.

OED.
Pragmatic:
Adjective,
Dealing with things sensibly and realistically in a way that is based on practical rather than theoretical considerations:
 

Reply to MICC Cable - phase to earth fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
431
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
920
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi gentlemen, I have three phase motor has an issue. This motor is star connection. When I just disconnect the power cable coming from MCC...
Replies
2
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
942

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock