Search for tools and product advice,

Discuss MPBC is it required in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
650
During an Eicr noticed the remote garage got an up & over metallic door.. the garage got its own CU & relevant RCBO’s… No incoming services only the newly installed Garage Door which is controlled by remote… would you consider a MPBC to it😂
 
I think the roller mechanisms on these (the tank style pulleys) are often plastic for this reason. Just do a continuity test from cpc to the door, see what you get.
 
Then it needs bonding. By definition of an extraneous conductive part.
It may not be, though. If the controller / motor unit is class 2 (which I'd wager it is) then it's not an extraneous part. No different to the now infamous crittal window scenario. In fact I'd go so far as to suggest that by bonding it you could be introducing a potential hazard where none previously existed.
 
It may not be, though. If the controller / motor unit is class 2 (which I'd wager it is) then it's not an extraneous part. No different to the now infamous crittal window scenario. In fact I'd go so far as to suggest that by bonding it you could be introducing a potential hazard where none previously existed.
Agree once again this topic always causes concern
MPBC if required would mean a TT system, it’s a report @ the moment & FI required
 
It may not be, though. If the controller / motor unit is class 2 (which I'd wager it is) then it's not an extraneous part
The motor is surely irrelevant, if there is a large lump of metal in contact with the ground (the frame of the roller shutter door) then it's most likely an extraneous conductive part (but would only require bonding if it's simultaneously accessible with any exposed conductive parts). There are other circuits in the CU, which may not be connected at the moment, but most likely will be at some point, probably including sockets.

It would be prudent to test it in any case.

For an EICR, I would suggest it's a C2 if it proves to be an ExtConPt.
 
The motor is surely irrelevant, if there is a large lump of metal in contact with the ground (the frame of the roller shutter door) then it's most likely an extraneous conductive part (but would only require bonding if it's simultaneously accessible with any exposed conductive parts). There are other circuits in the CU, which may not be connected at the moment, but most likely will be at some point, probably including sockets.

It would be prudent to test it in any case.

For an EICR, I would suggest it's a C2 if it proves to be an ExtConPt.
By that logic so is a garden gate!! My question remains - how, exactly, do you propose that this door is going to become part of an electrical circuit?
 
PME is not prohibited on a building site.
I think that’s an ish at best! So whilst 704.411.3.1 does not specifically prohibit it - outright - it does seriously discourage it, though. My view is that this Reg exists to allow PME supplies to be delivered to sites to get them going (with subsequent ‘normal’ deployment once construction is complete) but with the intent to not use the CNE aspect and make a TT instead. I also assume that as soon as the much discussed change to mandate foundation earthing systems comes into play then this Reg will disappear completely as irrelevant. Maybe. Just my take on it.

Meanwhile, back to this imminently lethal garage door……
 
By that logic so is a garden gate!! My question remains - how, exactly, do you propose that this door is going to become part of an electrical circuit?
Simultaneously accessible parts can be touched by a person, it’s internally & externally that could be the problem.Seeing industrial Roller Doors obviously these are actually attached to the main Metal Structure of the building which have a MPBC connected to it.
 
Simultaneously accessible parts can be touched by a person, it’s internally & externally that could be the problem.Seeing industrial Roller Doors obviously these are actually attached to the main Metal Structure of the building which have a MPBC connected to it.
Is the main building a metal structure?

If so then it ought to be bonded via something adequate (10mm equivalent, etc) but the actual doors are probably in pretty good contact with that already. A nulled wander lead, etc, should establish that.
 
My original reading of this was an automatic garage door, almost certainly earthed via CPC, so would it need separate bonding? Many of the above answers are right, but generally not establishing just what is actually risky here:
  • Is a bond needed to avoid shock risk between simultaneously griped parts?
  • Is any bond present large enough to avoid a fire risk under fault (open PEN) conditions?
  • Is the presence of PME connected metalwork a significant hazard?
As @mainline pointed out a quick check for the first point could be done if something is currently isolated, as they accepted threshold for let-go shock is about 10mA, and the body about 1k, so anything below 22k presents a risk if it is large enough to be grabbed and then unable to let go. Other situations might not result in paralysis, but they might result in another accident from involuntary movement causing a fall, cuts, etc.

However, to have a fire risk you need any extraneous part to be in good enough contact that more than, say 10A or so, can flow for long periods to risk a 1mm (or 0.75mm flex) CPC from overheating. So a typical outdoor light is almost certainly an extraneous conductive part as it will leak to the true Earth, but it ain't seeing tens of amps flowing so does not need a separate main bond!

Realistically if you attempted an Ra measurement and it is not below 20 ohms or so then its not needing 10mm bonds, though the regs don't specify anything beyond the bond size. I guess the implicit assumption here is the bonds considered are big stuff: metallic service pipes, steel structures, foundation rebar, lightning conductors, etc, any of which could well be in the 1 ohm or less territory.

The open PEN risk for general metalwork is one of those aspects that is sort of addressed by special areas, and now but EV charging under their own rules, but it has caused some serious risks before in situations that are still not addressed.
 
GN8 (6.3) Has this to say on the subject -

(701.415.2) Some insight into the subject of conductive parts that are not extraneous conductive parts can be gained from Regulation 701.415.2, relating to supplementary bonding in a location containing a bath or shower. Indent (ii) of the regulation states that metallic door architraves, window frames and similar parts are not considered to be extraneous conductive parts unless they are connected to metallic structural parts of the building.
 
PME is not prohibited on a building site.
Regulation 704.411.3.1 of BS 7671, which
states that a protective multiple earth (PME)
earthing facility shall not be used to provide
the means of earthing for a construction or
demolition site installation unless all extraneous-
conductive-parts are reliably connected to the
main earthing terminal.
Where consideration is being given to the use
of a TN-C-S system to serve a construction or
demolition site, reference should be made to
BS 7375 (see Notes in section 704 of BS 7671)
and to the relevant electrical distributor.
Although neither BS 7671 nor BS 7375 prohibit
the use of a TN-C-S supply, the Energy Networks
Association (ENA) state, in Section 6.2.2 of
Engineering Recommendation G12, Issue 4:
Requirements for the Application of Protective
Multiple Earthing to Low Voltage Networks that,
as it is usually impractical to comply with the
bonding requirements of BS 7671, a PME supply
should not be offered a construction site, except
for the supply to fixed buildings. As a result,
provision of a TN-C-S earthing system for a
construction site is highly unlikely and so an
alternative supply earthing arrangement must
be employed
 
From the ECA Technical Bulletin of March 2017:

How to determine if it is an extraneous-conductive-part, or not?

A simple measurement is undertaken. This is done by testing the resistance between the suspected extraneous-conductive-part and the MET or the nearest known connection to Earth, such as the circuit protective conductor (cpc) of a local circuit (so long as its connection to earth has been verified).

Published guidance by the IET suggests that if the ohmic value between the suspected extraneous part and Earth is greater than 22 kΩ, then the part in question is considered as not able to introduce a shock risk, and as such will not require bonding. To measure this sort of reading will require the use of the insulation resistance testing range (MΩ) where 22 kΩ will usually be displayed as 0.02 MΩ.

If the test reading indicates anything greater than 0.03 MΩ, then it may be concluded that the item in question is not likely to introduce a dangerous potential and therefore would not require bonding.​
 

Attachments

  • ECA Technical Bulletin - March 2017.pdf
    241.6 KB · Views: 1

Reply to MPBC is it required in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
961
Aside from every screwdriver in the universe, I wonder what the most creative mis-use of a tool you have encountered is. I'm sure this example can...
Replies
37
Views
4K
  • Article
Electrical2Go - Home Security: Using Floodlights, CCTV, and Door Entry Systems In an era where technology is advancing rapidly, home security has...
Replies
0
Views
280
  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
530

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock