Discuss My last 'non Amd 3' CU Install. in the UK Electrical Forum area at ElectriciansForums.net

Will have a flick through my books and see if I can dig it out


As an example - The first company i worked for had an office in a small industrial unit, TT installation with an upfront 100ma RCD, SWA sub-main from switch room to unit. A new consumer unit was put in the office we used and had 30ma RCD's. Both RCD's would operate in the event of a fault, Resulting in going to the switch room to reset.
 
Last edited:
Hmmmm, just gone to the page about selectivity in the book I'm currently reading and you guys are right - it says it should be s type in this case. In going to continue flicking through my books as in not sure what the hell I've read giving me this idea
 
Why type s? I thought 100ma would offer enough discrimination from a 30ma? Read somewhere 3 times as much, so for discrimination 90ma or higher should act independently without the need for a time delay

An S type RCD is also known as a time delayed RCD. If a 100mA RCD is installed upstream of a 30mA RCD, there will be no certainty as to which RCD will trip first. Cascading of General Type RCDs is therefore not recommended. Discrimination can only be provided by ensuring that the upstream RCD has a trip time and trip level envelope which is completely outside that of the downstream RCD. This can only be assured by using an S Type RCD upstream and General types downstream.
 
Last edited:
b377221ab2215e4587d2464b020b7692.jpg


Last paragraph is where I'd read it, doesn't mention s type until much later hence my confusion
 
p52 anyway that section is referring to mcb etc and that line is talking about discrimination between fuses/mcb

have a look at the table below (i thought i recognised the book ive got the 3rd edition)
Yep can see mcb, strange place to add an excerpt about rcd I think as all it did was throw me off
 
Why type s? I thought 100ma would offer enough discrimination from a 30ma? Read somewhere 3 times as much, so for discrimination 90ma or higher should act independently without the need for a time delay


Without knowing that this is not how you discriminate between rcd id like to know how you think youre in a position to offer advice on tt earthing systems?
 
Without knowing that this is not how you discriminate between rcd id like to know how you think youre in a position to offer advice on tt earthing systems?
Mate, see that thing under my name that says trainee? Cut me some slack OK? I wasn't saying I was right - merely stating my understanding which other members have kindly corrected me on. Not everything has to turn in to an argument, but I'm not sure you grasp that after having a glance through your posting history. Nearly everyone on here is extremely helpful, especially for people like me. I wish the same could be said about everyone, but comments like yours do the square root of jack all to add to this awesome outlet.
 
Without knowing that this is not how you discriminate between rcd id like to know how you think youre in a position to offer advice on tt earthing systems?
Hightower is a trainee which is clearly stated below his username and therefore is merely asking questions to better his learning.

**EDIT*** Hightower beat me to it but my point still stands!!
 
Last edited:
how? it is relatively easy in a lot of places to get a really low ra so why is an additional rcd needed in all cases

Well believe it or not its not there are people who out there who dont adhere to such high standards, theyll whack a 3/8 twig in on top of a mountain and leave with there big cheque, have seen in numerous occasions out in rural areas!
 
New posts

Reply to My last 'non Amd 3' CU Install. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
692
An interesting phone conversation with my own electricity supplier (Good Energy) which was very disappointing, and made me sigh (professionally)...
Replies
23
Views
9K
I do seem to pick only the weirdest properties to inspect... Victorian terraced house today - with up front RCD to a Wylex fuse board and main...
Replies
24
Views
3K
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
13K
Hello, Would like some opinions. We have quite a few CU upgrades to complete. These are PRS properties, and looking down the list, a lot will be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock