OP
Vol
Hi Pete999, here is a partial screenshot of a page of the doc.
Discuss New Consumer Unit Installation - L&N Reverse at the sockets in the The Welcome Forum area at ElectriciansForums.net
file:///C:/Users/Pete/Downloads/BS_7671_2008_AMD3-2015_Model_Forms(3).pdfOther values I can see:
Nominal frequency: 50Hz
External earth fault loop impedence Ze (2/3): 0.57
Prospective fault current (2/3): 0.5
the report also states that he used for testing equipment, a Kewtech KT64 (might be 84, hard to read)
Page5of6 schedule of test resultsNot sure how to download files. However, here is a link to almost exactly the same form, I say almost because the layout of Scheduled Inspections has changed but not the content I don't think. This is the form. If you can show me where to see where those values should have been written then thanks.
http://www.electricaltestcertificat...estic-Electrical-Installation-Certificate.pdf
2nd line down LtoL IR over 200 Mohms that would indicate you have a 3 phase supply
to be fair, i'd put that down as a typo.2nd line down LtoL IR over 200 Mohms that would indicate you have a 3 phase supply
Not sure why he's put N/A for continuity of protective conductors?
I've never got rcd test results that low hahaSome circuits are run surface and should be rectified in future ?
Whats the world record for speed of reaction of a 30 m/amp Rcd ?
200 M/ohm across the board seems like a very common reading for insulation resistance of well used installations these days
The consumer unit is a 11 way,the test schedule lists 5 ways,the 2 Rcds seem to have 3 circuits each ,decisions,decisions,try as I will,I just can't make sense of what has been produced
I feel vilified
Tails in photo don't indicate that. Personally I don't like exposed live bus bars either.3 phase supply
I've never got rcd test results that low haha
0.02 and 0.03 of a second
Edit
Or is it 0.2 and 0.3 of a second I can't make it out?
Just pointing out that either it was a typo (very likely) or the report is a fudgeTails in photo don't indicate that. Personally I don't like exposed live bus bars either.
Just pointing out that either it was a typo (very likely) or the report is a work of fiction
Reply to New Consumer Unit Installation - L&N Reverse at the sockets in the The Welcome Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.