I was trying to replace a broken built in oven which was a hardwired 13amp cooker which was on its own circuit along with a hob (32amp RCBO). The replacement oven was also a 13amp cooker but i have been told i would not be able to replace it with a 13amp oven now and that it would have to be fitted with a plug and then a plug socket would have to be installed as regulations have changed.

Is this true? If a hob and oven are on the same circuit then what amp oven could be hardwired?
 
I was trying to replace a broken built in oven which was a hardwired 13amp cooker which was on its own circuit along with a hob (32amp RCBO). The replacement oven was also a 13amp cooker but i have been told i would not be able to replace it with a 13amp oven now and that it would have to be fitted with a plug and then a plug socket would have to be installed as regulations have changed.

Is this true? If a hob and oven are on the same circuit then what amp oven could be hardwired?
 
So where did you plug the original cooker, who told about the new regulation?, some teenager in Currys
 
The original cooker is hardwired behind with a connection unit and is then connected to an isolator switch above the hobs.
I was told this by a white goods installer. He said 13amp cookers could no longer be hardwired. Why i don't know. If both cookers are 13 amps could they not be swapped like for like
 
The original cooker is hardwired behind with a connection unit and is then connected to an isolator switch above the hobs.
I was told this by a white goods installer. He said 13amp cookers could no longer be hardwired. Why i don't know. If both cookers are 13 amps could they not be swapped like for like
 
Then your best bet is to get the services of a local Electrician, might cost a bit over the festive season
 
Has the new oven got a plug on it and can you show a pic of the existing connection.
White goods installer that is a new one.
 
The original cooker is hardwired behind with a connection unit and is then connected to an isolator switch above the hobs.
I was told this by a white goods installer. He said 13amp cookers could no longer be hardwired. Why i don't know. If both cookers are 13 amps could they not be swapped like for like
I'll buy it WTF is chuntown?
 
White goods installer ..... Who probably not got any qualifications, experience or test kit.........

Sounds like a Currys delivery driver
 

Reply to New cooker installation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
705
Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Replies
1
Views
947
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
817
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
798

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock