Have a job coming up to supply a new distribution board. I am planning on running a 25mm 4 core swa and 16mm earth of a distance of 30mtrs from incoming supply to new board. The supply is 3 phase 100a tncs. I was thinking of coming out of the Henley blocks into a 100A Glasgow switched fuse and then the swa out of the switched fuse to a 80A 30mA 4pole rccb supplying the new board. Thoughts?
 
I find it good practice to run a separate earth instead of using the swa. The rcd would be positioned below the board then tails out of it into the main switch. Reason for rcd is because it is a production area with access to outside where outdoor equipment may be used.
 
I find it good practice to run a separate earth instead of using the swa. The rcd would be positioned below the board then tails out of it into the main switch. Reason for rcd is because it is a production area with access to outside where outdoor equipment may be used.

An extra earth is completely unnecesary, but whatever that's your choice.

One RCD covering the whole DB ? What size is the proposed DB and how many circuits and of what nature and use are the final circuits ? Do you think this will comply with the regs ?
 
my standard set up would be, tails to switchfuse unit, swa to distribution board with main switch then rcbos for circuits that require it, or even better if containment allows, rcd socket outlets and no rcd potection at db at all

swa as cpc

if its to supply machines used in production, the last thing you need is that rcd mainswitch knocking out the whole area every time you get a small problem on one circuit

and why would you have it as a stand alone unit rather than as part of the db?
 
Last edited:
I know what your saying, but as usual it's all down to cost. A 32A TP socket with rcd is around £360.


Well if cost is the issue, then you need to give the customer the options(with the possible negaitive effects of cheaper choices)

and let him decide, and put it in his court when or if there are any issues later on

you dont want the phone calls in a months time that the machines are abit leaky and keep knocking out the whole board!

if you give him the choice at the start, problems afterwards are billable! ;)
 
I know what your saying, but as usual it's all down to cost. A 32A TP socket with rcd is around £360.

No it's not all down to cost it's about appropriate design and compliance with the regs.
Is that what price you have been quoted for a 32A RCD socket ? because if you look around they should easily be less than a hundred each.
RCBO is not an expensive solution is it ?
 
http://www.neweysonline.co.uk/mk-electric-single-socket-outlet-prewired-30ma-rcd-protected-tp%2Bn%2Be-32a-380-415v/1050079403/ProductInformation.raction
 
Haven't the regs to hand but I'm guessing minimum disruption?

I think if you are designing a commercial production area installation and you are not aware of the requirements you are going to need your regs at hand.
Also if you are pricing a job using random internet prices instead of getting accurate quotes from wholesalers you're going to price yourself out of the job anyway.
 
The job isn't for a while yet so haven't sat down and designed it yet. Was just getting opinions and suggestions. 2 heads is better than 1 and all that! I only use the internet for rough ideas on prices. I will get a quote from wholesalers once I have it designed. It will be inline with the regs as is all my work, so yes will have it at hand once I get the time to sit down and plan it out.
 
First thing is check if rcd protection is actualy required there are ways of designing the installation so that rcds are not required , im not saying you won't need rcds but look at alternatives first
 
Cost can be argued against lost production, if you have a fault you have lost the whole production area with your design, yes these outlets are costly but to comply to regulation regarding disruption then you have to explain this to the customer, having done commercial and industrial most of my career, I would never fit a 30mA front end on a distribution board unless special circumstances exist and/or it was otherwise requested by a designer of the install if that wasn't you - even then I would be holding a meeting to express my concerns.

The extra's to have RCD protection at the point of load where upfront protection isn't needed for cables etc may be thousands of pounds but to lose half a day or more production while an electrician comes to clear a fault they cannot isolate would probably dwarf the cost of designing it correctly in the first place, if this is about saving a few quid then you need to have a sit down and talk with the customer.
 
i wouldnt bother with an rcd but thats not to say i might not have a safety circuit that can shut large amounts of the installation out.

most industrial installs dont need an rcd.

why do you need an rcd? most machines have multiple guards/barriers to keep the operators away from the cables etc.

a company would rather pay £2000 than 200 if it means they wont be getting nuisance tripping causing a high loss of production
 
Nothing is confirmed yet I only met the client the other day so still a few meetings etc. before anything is finalised.
 
The companys method statement should say somthing in the Lines of Isolate the equipment before cleaning , do not use high presure water on equipment etc.
 
Have a job coming up to supply a new distribution board. I am planning on running a 25mm 4 core swa and 16mm earth of a distance of 30mtrs from incoming supply to new board. The supply is 3 phase 100a tncs. I was thinking of coming out of the Henley blocks into a 100A Glasgow switched fuse and then the swa out of the switched fuse to a 80A 30mA 4pole rccb supplying the new board. Thoughts?

16mm separate earth is most likely oversized and a complete waste of time and money to boot, if main bonding is required at the sub-board then a 10mm bond will be required, but not if no main bonding is to be connected there.
Glasgows are fused switches not switched fuses, there is a difference.
An 80A RCD is no good on a 100A supply.
A 30mA RCD covering a whole board is just plain ridiculous.
 
I mean when the cleaners are in they hose down everything

So make sure the install meets the appropriate IP rating, or is put into suitable enclosures. An RCD won't stop anything from getting wet, it will just switch it off and water will continue to enter the equipment.
 
I think the best option is use individual rcds if required. So instead of the 16mm earth would you just use the swa?

Using a seperate earth for the size you suggested wouldn't normally be required although it may be necessary in certain circumstances like reducing Zs due to high upstream initial values or bonding requirements may warrant running a seperate earth.
 
I think the best option is use individual rcds if required. So instead of the 16mm earth would you just use the swa?

Yes, following on from carrying out the calculations I would use the armour. If the armour is not sufficient then I'd look at using a bigger cable or a fifth core within the cable.
 
Had a look at the current set up. There is a main DB and 2 sub DB's. 1 of the sub boards is supplied from a fused switch and the other one is supplied from a 63A TP MCB. I would have thought both sub boards would have been supplied by fused switches.
 

Reply to New dist. board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
298
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
902
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock