Discuss New house - does the CU comply to the current regs in the UK Electrical Forum area at ElectriciansForums.net

A new build wouldn’t have channelled wires as the cables would be clipped direct to the fabric of the building then boarded over.
If the cables have capping over them then without knowing any other installation details such as insulation in stud walks which could make it reference method 102 or even 103 , I would say method C for capping or direct clipping.
Oval conduit enclosing the cables then maybe method B.

There’s not that much difference between them in terms of ccc, life’s too short to be worrying about reference methods. :)
 
Last edited:
5 seconds if it’s feeding a second DB. 0.4 if it is a final feeding sockets. Assuming TN system.
 
Method B could be if cables down to C.U. in bit of trunking and put down as most arduous condition, in oval conduit or has classed capping as method B.
Circuits, not RCD protected maybe cables over than 50mm of surface
or capping to comply with reg 522.6.204 (iv) I can't see the other methods used.
 
IMHO - if there really is 10mm swa into the metal CU that's probably the only circuit to qualify for high integrity position, pending what's been done in the shed. Rest of it will be "cables in walls" from CU, surely ?
 

Reply to New house - does the CU comply to the current regs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
579
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
911
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
277
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
653
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
764

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock