Can someone confirm, if there is a code number under BS standards that the work needs to be good workmanship.

The problem is defining what constitutes good workmanship. Untidyness is less than ideal, but not problematic in itself.

A small amount of sealant and some grommet strip solves the tails issue and a few clips to provide adequate support on their route up to the board (if not already in place). It's difficult to discern other issues from the image provided.
 
Was he incorrect in then specifying and quoting for a dual rcd board from contactum (spelling). I merely wanted a better brand.

The general consensus will be that dual RCD boards should be avoided and I'd fully agree with that.

It's worth pointing out that Contactum is not a cr*p brand as per your previous statement. Contactum or Hager would have been perfectly good options with RCBOs in place of the current dual RCDs, although as @timhoward points out CP Fusebox provide a very good value alternative.
 
@westward10 my understanding is that they look like this - and I'd expect to see some glimpse of the CPC .
View attachment 105116


That wasn't the wisest move really.

What did he want to fit? Was it Fusebox? Any RCBO board would have been better.
If you supplied the board how did he end up with exactly the right number of B6 breakers for lighting unless you also knew the plan in advance?

The main reason is that the regs encourage us to design to limit cumulative earth leakage and specifically tell us to consider RCBO's in residential premises. (Section 314 and section 531.3.2 )
If he had recommended, a RCBO and the reasons for it, i'd have it done. His quote states "1. Supply and Installation of x 1 Dual RCD Consumer unit with SPD' He told me the brand was contactum. I wanted Hager or schneider.

As to the B6 breakers, as I bought a much bigger board I knew there would be gaps. Also I wasn't sure if each smoke detector needs its only 6 amp breaker so thought best to buy extra of those. They are only 3 pounds and a blank is over` £1. I thought it wise to buy those, but I also have 5 extra mcb's not fitted which I can take a photo of, a 6, 16, 20, 20, 32. So I bought a mixture.

I have it in writing, that the plan is to have a ground, 1st floor, and loft where the circuits are 32 amp, and lighting is 6.
I asked about the smoke detectors running off the 6 amp for the lighting, and was told it will be on a "separate circuit from the consumer unit not from the light".

Well it is connected to the same circuit breaker that does the kitchen lights.
 
The general consensus will be that dual RCD boards should be avoided and I'd fully agree with that.

It's worth pointing out that Contactum is not a cr*p brand as per your previous statement. Contactum or Hager would have been perfectly good options with RCBOs in place of the current dual RCDs, although as @timhoward points out CP Fusebox provide a very good value alternative.
Fair enough - every electrician I asked said they wouldn't go near contactum, and I already had a Hager so thought it makes sense. Secondly where do you keep getting RCBO's from? The quote was for a dual RCD board. RCBO's were never mentioned, perhaps if I had been told the benefits I would have bought them.
 
If he had recommended, a RCBO and the reasons for it, i'd have it done. His quote states "1. Supply and Installation of x 1 Dual RCD Consumer unit with SPD' He told me the brand was contactum. I wanted Hager or schneider.

As to the B6 breakers, as I bought a much bigger board I knew there would be gaps. Also I wasn't sure if each smoke detector needs its only 6 amp breaker so thought best to buy extra of those. They are only 3 pounds and a blank is over` £1. I thought it wise to buy those, but I also have 5 extra mcb's not fitted which I can take a photo of, a 6, 16, 20, 20, 32. So I bought a mixture.

I have it in writing, that the plan is to have a ground, 1st floor, and loft where the circuits are 32 amp, and lighting is 6.
I asked about the smoke detectors running off the 6 amp for the lighting, and was told it will be on a "separate circuit from the consumer unit not from the light".

Well it is connected to the same circuit breaker that does the kitchen lights.

The above is one of many reasons why a lot of electricians insist upon supplying materials - or at the very least writing a comprehensive list.

Your new board is not what many would recommend, for reasons previously outlined, but having a dual RCD board doens't present any inherent danger. It can be argued that such boards should no longer be fitted, and I'd be the first to argue that very point, but changing it again will present significant cost and this would be borne by you as the board was your choice.

Provided the wiring in your home is good, and connections sound, the risk of problems should be exceptionally low and it might be best to get any real issues resolved and chalk the rest up to experience. I doubt you'll be using this electrician again, but in future would look for word of mouth recommendations or ask for someone local on a specialist forum like this one.
 
Was he incorrect in then specifying and quoting for a dual rcd board from contactum (spelling). I merely wanted a better brand.
It's a slightly subjective one. "RCDs shall be selected and the circuits subdivided in such a way that any earth leakage current likely to occur during normal operation of the connected load will not cause unwanted tripping of the device"
One might argue that stacking 8 (or 7 and a spare?) circuits on a single RCD is pushing it a bit.
On the other hand if he measured the normal leakage current as <=9ma then he's complied with a further ident of the same reg.

I think you've had good advice already. It's not neat and tidy, it could use some cable restraint, and wiser decisions could have been made laying out the board. They look like Type A RCD's, it has SPD protection and it's a decent brand.

It sounds as though you have had an almost complete rewire for a pretty decent price for London.
The smoke alarm setup is probably in fact a good idea as if that circuit trips you will know about it as it is also feeding lighting.

I actually can't see an NICEIC complaint getting far with this one, we've seen much worse on here and their first response will be to ask you to put your complaints in writing to the sparks anyway. They will only get involved (and reluctantly) if relationships completely break down or he refuses to address your complaint.
I'd suggest a civil conversation with him to request he tidies up a bit, and double check there's a CPC wire in the SPD.
 
Fair enough - every electrician I asked said they wouldn't go near contactum, and I already had a Hager so thought it makes sense. Secondly where do you keep getting RCBO's from? The quote was for a dual RCD board. RCBO's were never mentioned, perhaps if I had been told the benefits I would have bought them.

I can't think of any reason why they might make such a statement or why you'd heed their advice about boards, while not having them work in your home. Certainly not my first choice of board, but that's not down to quality - as it happens, there's a Contactum board less than 6 feet from me as I type.
 

Reply to New rewire and fuse board - views on work. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
864
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock