That DOES NOT answer my question, the question that has haunted this thread for pages

Please answer my question ......
That is the answer......134.1.1 and you don’t understand because you have’nt got enough experience or training. There’s only 2 places I can name where you insulate SWA from connection.

Using VSD’s
And leaving equipotential zones.
 
Sorry mate, but you have now gone beyond my simple mind. I've read the references you've kindly provided and I can't see a problem using an already in place TNCS/PME DNO cutout to supply the shed. No going to jail that I can see, provided it's done in accord with our usual BS7671. What have I missed ?
That ‘given earth’ is for ‘that equipotential zone’

You won’t understand because you can’t grasp the importance of an equipotential zone on a tncs supply. So I 100% know you will never understand. So will stop there with you.
 
The question was and still is WHERE DOES IT STATE THAT THE ARMOUR MUST BE CONNECTED TO EARTH AT THE SUPPLY END
Because it is in the HOUSE and running through the fabric of the HOUSE and in the HOUSE equipotential zone...because it’s an extraneous conductive part.....and not with a strap but with an SWA gland 134.1.1
 
The thing about Bigbob1 and his arguments, is that they are not based in fact and he cannot back up anything he states.
If a law of physics prevents us from doing something, permission from the DNO will not suddenly allow us to do it.
GN5 (although my copy is from 2004) makes no mention of us not being allowed to export any earthing system.
Same applies to ESQCR and EAWR.
In fact, ESQCR requires the DNO to allow me to export the earthing system, the only reasons they can refuse is if the installation does not comply with BS7671, is unsafe or if it might cause a disruption in network supply.
 
Because it is in the HOUSE and running through the fabric of the HOUSE and in the HOUSE equipotential zone...because it’s an extraneous conductive part.....and not with a strap but with an SWA gland 134.1.1

Look you clearly don't seem to realise [or care] that there are many well qualified,highly experienced and dedicated professional electricians on this forum. Nowhere has it been suggested using a strap instead of an SWA gland, although this was common practice for many years and I'd imagine considered acceptable at one time. Of course the armour must be connected to earth, you do realise that we're talking about situations where a seperate CPC is used within the cable ? But I still say that it doesn't state anywhere that the armouring MUST be earthed at the supply end. I've had enough of this nonsense now and won't post any more on this thread.
 
Anyway where is this place we are exporting things to? Will we be able to export them when we leave the EU? Arghhhhhh..........
Or did you mean extending??
 
Look you clearly don't seem to realise [or care] that there are many well qualified,highly experienced and dedicated professional electricians on this forum. Nowhere has it been suggested using a strap instead of an SWA gland, although this was common practice for many years and I'd imagine considered acceptable at one time. Of course the armour must be connected to earth, you do realise that we're talking about situations where a seperate CPC is used within the cable ? But I still say that it doesn't state anywhere that the armouring MUST be earthed at the supply end. I've had enough of this nonsense now and won't post any more on this thread.
An extraneous conductive part in a house doesn’t need bonding to earth.......kind of invalidated most of your last and final comment.
 
I'll have to reply again, what I'm saying is it CAN be connected to earth at the far end - as long as it's connected. You're clearly less intelligent than you think you are.
 
New posts

Reply to New sub board for shed swa advice. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
1K
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
990
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
772
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock