Cheers Gavin. I don’t get precious about constructive criticism. I kind of expected what the response to the post would be.

Hi Murdoch 100Amp BS7671. Was 25mm already to meter from fuse. I upgraded to 25mm from 16mm load side of meter. Main Earth already 16mm, bonding to gas and water already 10mm.
 
Agreed. Can’t see the point of upgrading half of the supply. Dangerous also.

Disagree 100%

there is no way any normal residence in the UK is ever going to pull 84 amps long enough to burn out the tails.

You can use the maximum load to justify not upgrading and be VERY careful removing seals from the meter.
 
Disagree 100%

there is no way any normal residence in the UK is ever going to pull 84 amps long enough to burn out the tails.

You can use the maximum load to justify not upgrading and be VERY careful removing seals from the meter.
wash your mouth out with soap... removing seals from a meter... as if anyone would contemplate that.... oops, seal fairy just whisprered in my lug hole.
 
would that not get pulled in an assessment though?
No as cutting a seal off would be classed as criminal damage. There's a lot of risk involved in pulling a DNO fuse hence the reason why they like to charge us vast amounts of money to do it for us.
 
No as cutting a seal off would be classed as criminal damage. There's a lot of risk involved in pulling a DNO fuse hence the reason why they like to charge us vast amounts of money to do it for us.

Depends on the DNO; SSE allow removal of their main fuse by sparkies in a scheme, not Stroma 'cos they don't charge enough!

Verify your DNO policy OP.
 
One option as a temporary measure with the N break would be to reduce the OCPD rating to 20a leaving the circuit as it is. An explanation could be provided on the EIC that the circuit has been protected from overload and investigation and repair will be carried out at a later date on the clients instruction.
If it was not practical to fix before the NIC visit thats what I'd do.
 
Thanks Wirepuller,
That’s something worth considering as time isn’t on my side. Do you think that would satisfy the assessor?
Cheers
i'd think that would be OK as you would have shown that you'd done everything possible to minimise the risks, and that it's the customer who has the final say on whether he's prepared to pay for a permanent fix. but get it on paper.
 
Do you know which sockets/outlets the break is between? as if you intend to change the protective device to 20A the NICEIC will take a dim view of the live being left as a ring you will need to test as two radials below earth loop limit. The loading, diversity and distribution of
the sockets would be a factor especially as it is feeding the kitchen.
 
The kitchen actually has two rings to it. As is an old extension and assuming from when this was done. I haven’t established which outlets the break is between yet.
 
The most common reason for a "break" in a ring is a lose connection at a socket or fused spur

Shouldn't take long to locate.......
 

Reply to No cpc on lighting and no neutral continuity on kitchen ring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
839
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
633
Just to be clear… I am going to do the correct thing here and pay for the correct parts…. I just wanted to start the discussion. My particular...
Replies
6
Views
245
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock