Discuss No cpc on lighting and no neutral continuity on kitchen ring in the UK Electrical Forum area at ElectriciansForums.net

If there is no R1 + R2, it's pointless to have an RCD. Earth continuity, is a must. RCDs are for earth faults. You tell Mrs Jones that you replaced her board with an up to date version but will not have the benefits of a new version, but it's fire protected because it's metal. Might as well change the 3036 fuses to wylex switches in that case, it's more practical.
 
This is irrelevant to this thread - the OP's doing a CU change , not an EICR
Exactly, there can not be any C1 or C2, otherwise he cannot issue an EIC. All has to be earthed and all mcbs and RCDs need to meet the requirements of the regs. I will never issue a EIC knowing that's the earthing to the lighting is not in place and I will tell Mrs Jones, I cannot continue with the board unless she pays me to rectify the issues that will prevent me from issuing an EIC, because I am the one responsible by law, I am the one who signs off the work and I am the one who notifies building authority.
 
Exactly, there can not be any C1 or C2, otherwise he cannot issue an EIC. All has to be earthed and all mcbs and RCDs need to meet the requirements of the regs. I will never issue a EIC knowing that's the earthing to the lighting is not in place and I will tell Mrs Jones, I cannot continue with the board unless she pays me to rectify the issues that will prevent me from issuing an EIC, because I am the one responsible by law, I am the one who signs off the work and I am the one who notifies building authority.
Bs7671 does not require existing circuits to be upgraded unless they are defective or non-compliant with BS7671 in a way that they would result in the installation being dangerous. There is no legal requirement for the existing to be upgraded.
Suggest Sham reads Electrical Safety First, Best Practice Guide No 1, Replacing a Consumers Unit in Domestic and similar premises. Sorry Muzza
 
Last edited:
Bs7671 does not require existing circuits to be upgraded unless they are defective or non-compliant with BS7671 in a way that they would result in the installation being dangerous. There is no legal requirement for the existing to be upgraded.
^^

I am guessing you are NICEIC member ....
No, but used to be a Duty holder/Q.S.you don't need to belong to a shame, scheme etc to do things correctly.
 
Bs7671 does not require existing circuits to be upgraded unless they are defective or non-compliant with BS7671 in a way that they would result in the installation being dangerous. There is no legal requirement for the existing to be upgraded.
But I'm sure you can not change a fuse board if earthing not correct. It defeats the object. If an inspector asks you to carry out an RCD trip test, you are in trouble
 
Bs7671 does not require existing circuits to be upgraded unless they are defective or non-compliant with BS7671 in a way that they would result in the installation being dangerous. There is no legal requirement for the existing to be upgraded.

No,but used to be a Duty holder/Q.S.
Ignore my last post about NICEIC Ant, thought Murdoch was referring to the OP didn't see the arrows aimed at your post.
I'm out of this one.
 
. Apparently you could get away without CPC to lighting before, as long as there are no metal switches or fittings. That's all changing now.[/QUOTE]
What is changing?
 
Suggest the OP reads Electrical Safety First, Best Practice Guide No 1, Replacing a Consumers Unit in Domestic and similar premises.
Suggest Sham reads Electrical Safety First, Best Practice Guide No 1, Replacing a Consumers Unit in Domestic and similar premises. Sorry Muzza[/QUOTE

You can not there fore issue an EIC then.
From Electrical safety First
4.3. However, circuits that are defective or non-
compliant with the requirements of BS 7671 in a
way that would result in immediate or potential
danger must not be reconnected to the consumer
unit.
.
 
Suggest Sham reads Electrical Safety First, Best Practice Guide No 1, Replacing a Consumers Unit in Domestic and similar premises. Sorry Muzza
From Electrical Safety First
However, circuits that are defective or non-
compliant with the requirements of BS 7671 in a
way that would result in immediate or potential
danger must not be reconnected to the consumer
unit.
 
What is changing?
You cannot report it as an c3 and advise no metal fixtures, there has to be a CPC connected.[/QUOTE]

The definition of the codes used on eicr are not changing, and neither are the requirements for cpcs. This issue will be no different on a periodic inspection in the 18th to what it is now.
 

Reply to No cpc on lighting and no neutral continuity on kitchen ring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
837
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
633
Just to be clear… I am going to do the correct thing here and pay for the correct parts…. I just wanted to start the discussion. My particular...
Replies
6
Views
230
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock