Discuss No power to whole house after water fell on to cooker??? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
A friend has just called as his daughter in Belfast (many, many, many miles from me!) has just lost all power after water fell into the cooker/hob.

I straight away thought it has to be a main RCD somewhere, but I cannot see one in the pictures they have sent and they don't 'think' there is one.

I realise the main switch is switched off on the BS3036 fusebox, they have said it is on now, but still no power anywhere, although I am getting them to confirm if they really mean everywhere as I can see a separate consumer unit doing the shower, so I have asked them to find out if power to the shower. Also, the old black BILL unit supplies the garage, so i have asked them to see if power in the garage.

update... no power to absolutely everywhere (including shower and garage)

Perhaps the main cut out? Really unlikely, but possible.

CU1.jpg CU2.jpg CU3.jpg
 
Obviously the cooker circuit needs checking before re energising
 
Looks like no display on the meter. If so no power to it.
So Either a power cut or the main fuse has decided to jack it all in and shuffle off this mortal coil.
 

Reply to No power to whole house after water fell on to cooker??? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
841
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
925
In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
409
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
Replies
3
Views
794
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
271

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock