Discuss not getting 240v in the Australia area at ElectriciansForums.net

C

chrisgb82

im a builder just finished refurbishing a house and had a call from the house owner saying hes only getting about 195 volts out of his living room sockets does anyone know why this could be?
 
Have you rang the spark who installed them? You could have a loose connection between the sockets. Could be a supplier problem if its throughout the installation!
 
Last edited by a moderator:
seen as you only said living room i would say Loose Connection 100% probably a neutral

check incoming supply voltage to ensure DNO is upto scratch to be on safe side though
 
ill check its def only living room but thats what i was told over the phone, so a loose connection can def make you lose voltage ? i didnt realise this could affect voltage but thanx
 
so can this be tested in a way that we dont have to remove all socket fronts (theres 11 doubles in the living room alone)?

Wow, 11 in one room??? Is this a mansion??? Yes it can be tested at the midpoint and then halfed again until its found. You are looking at opening a few socket fronts though!
 
You could try and find the mid point of the ring using r1&r2 calcs but in all honesty I would remove all the fronts and check all the connections,don't mess about as you may find other loose connections there.It happens to everyone but I would say the testing side should have picked this up?
 
If you are dropping voltage,best get it sorted and tested

Low voltage and modern electronic equipment and appliances dont make good bedfellows
Could become an very expensive problem
 
how the hell would a customer who i am assuming has limited electrical knowledge be able to tell what voltage he is getting in the lounge....I mean i went to college for 3 years got all the bits of paper to wave round and now customers are telling us what kind of voltage they are getting...????????
 

Reply to not getting 240v in the Australia area at ElectriciansForums.net

Similar Threads

Hi everyone. The title should sound crazy enough, but it's what happening in my 72-years old home we've purchased 2 years ago. I found the crazy...
Replies
1
Views
483
I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
692
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
569
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock