Discuss old installation! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

johnboy6083

-
Esteemed
Reaction score
1,597
The other day, i was installing a new circuit from an old 3ph DB, and i was working for an agency, subbing me out to a company who install specialist equipment (wont mention what because dont want repercussions).
We were running SWA out of the board on tray to the items of equipment.
when i saw the old board, there were no blanks fiitted, even though they were needed. The supply is TNS, but the main earth from that was only 10mm. No lid on the trunking containing the cores of the paper insulated cores from the supply. This is in a wooden cupboard, in a car park, accessible to the public.

When i mentioned that we sort it out, the company sparks i was working with, said not to worry, cos we will test our circuits ect, and the rest of the installation is not our prob.

Ive now finished there, but what would be the correct course of action, if i ever come up against that again?

would i report it to the client, and then refuse to issue a cert? Would i issue acert for our new circuit, but note the limitations of the inspection?

John
 
Last edited:
I dont work in commercial/industrial but from what I understand you are only liable for the work that you do. If I came across anything on an installation I was working on that I thought was unsafe then I would tell the customer and recommend sorting it out in writing, and I would also put a note on the cert in the comments box highlighting the problem. That way youve covered yr arse:)

Also the main bonding should always be bought up to current regs before any work is carried out.
 
Last edited by a moderator:
You are responsible for anything on the existing installation which will affect the safety of the addition or alteration you are carrying out,this may include inadequate main bonding,main earth,missing trunking lid if you are using that trunking etc.
This is why you must be careful on a cert to specify exactly the extent of the work carried out. Most people would note any defects found ,which need to be rectified but do not affect the safety of the work carried out.
 
Last edited by a moderator:

Reply to old installation! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi I always thought installations were safe at the time of instalment etc, the Distribution Boards at my works were installed over ten years back...
Replies
7
Views
887
Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
634
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
457
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
409
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock