Discuss Only 38 years without an earth. .. in the UK Electrical Forum area at ElectriciansForums.net

O

Octopus

One of my neighbours has just had an electric door fitted. The fitted commented that the garage didn't have an earth .... so I have just had a look

Sure enough 2 core SWA runs from a SFCU in the lounge (not glanded to the back box) out to the garage where the SWA is glanded to the back box.

SO I'm thinking that either

A. I run a new 3 core cable from the house to the garage (less than 1 metre) or

B. I run a 4mm CPC (in protection) from the SFCU to the garage ..

B is cheaper ........... anyone want to give me a reg number why I can't do it this way?
 
Yup B, who cares about reg numbers, it will work fine.
 
why not earth the SWA armour at the SFCU?

Customer doesn't want me making a big hole in the wall:)

Yup B, who cares about reg numbers, it will work fine.

Very amusing - not.;)

I'd put a new cable in. 1mtr? You could've done it in the time it took to post the question.....;)Hardly going to be much cost difference either way.

A small matter of a concrete path in the way means its not that easy...

Hence the post.:)
 
tell them it takes hammer to crack a nut . walk away .if they don't want it done ,I keep falling out with my neighbours because they always want the jobs done for nothing .my name is not jack been up the bean stork .
 
tell them it takes hammer to crack a nut . walk away .if they don't want it done ,I keep falling out with my neighbours because they always want the jobs done for nothing .my name is not jack been up the bean stork .

Paying is not an issue given their impeccable record ....
 
Is the 2 core visible on the outside of the house wall before it goes into the wall?

Just thinking that if you can intercept the 2 core between house and path, cut it and gland into new enclosure on outside wall, and run new cable into back of FCU? Could use TnE in conduit, so no disturbance to internal plasterwork, no digging up of path?
 

Reply to Only 38 years without an earth. .. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
488
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
919
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
701

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock