Discuss OSO hotwater boiler_Issue heating the water in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
I currently rent a flat, which uses an OSO hotwater boiler to heat the water but it seems there is an issue heating the water and I thought to ask here in case anyone would have an answer before I ask my landlady to call an electrician.

Attached is an image of the boiler on Pic1 and on Pic2 is the switch with a timer (in red circle) which is linked to the boiler.

The issue is that whenever I take a shower and use all the hot water then there is no hot water until the next day. I asked the concierge in the building and they told me I need to move the switch of the timer to the “permanent” position so the boiler can heat the water instantly.

It’s been a week since I did this, but it seems the issue still persists. For example, the other day I took a shower at 1pm and used all the hot water. I then went to take another shower at 10pm and there was no hot water. There was enough time in between for the boiler to heat the water, but that didn’t happen.

Does anyone know why is this happening?
 

Attachments

  • Pic1.jpg
    276.6 KB · Views: 57
  • Pic2.jpg
    333.8 KB · Views: 50
I would turn on the switch marked water heater it looks like the tank has 2 heating elements the lower one should be controlled by the night immersion switch and a night time economy 7 tariff the top element should be controlled by the water heater switch and the timeclock this would heat the water during the day to whatever program is set on the time clock
 
I would turn on the switch marked water heater it looks like the tank has 2 heating elements the lower one should be controlled by the night immersion switch and a night time economy 7 tariff the top element should be controlled by the water heater switch and the timeclock this would heat the water during the day to whatever program is set on the time clock

So, if only the "Night Immersion" switch is on at the moment, then at what time does the system start heating the water?

By the way, I don't know if this matters but my electricity is with British Gas and I'm on the pay as you go tariff like I have a prepayment meter. So, I don't know if the economy 7 tariff is applicable in my case.
 
So, if only the "Night Immersion" switch is on at the moment, then at what time does the system start heating the water?
Economy 7 is usually 7 hours of cheaper electricity between midnight and 7am although these times can drift a bit to prevent a large network surge
By the way, I don't know if this matters but my electricity is with British Gas and I'm on the pay as you go tariff like I have a prepayment meter. So, I don't know if the economy 7 tariff is applicable in my case.
Can you post a picture of the electricity meter and the cables connected to it so we can possibly identify how it is working
 
Last edited:
Economy 7 is usually 7 hours of cheaper electricity between midnight and 7am although these times can drift a bit to prevent a large network surge

Can you post a picture of the electricity meter and the cables connected to it so we can possibly identify how it is working
I'm new to the flat and I'm still trying to find where the electricity meter is. I don't think it's in my flat, because the only thing with numbers is that panel where I put the electricity key to transfer the money so I can have electricity in the flat.

I wanted to ask the concierge today for the meter, but he was never in the office. So, next time I find it I'll post a photo. For now, I took the below photo if that helps with the cables etc.
 

Attachments

  • Pic3.jpg
    364 KB · Views: 42
Can you post a picture or two of all the electrical controls on the right hand wall of the cylinder cupboard it looks like you have a mains isolator and a service head so where you put the electricity key is likely to be the meter
 
Hi All,

I'm wondering if anyone could assist with another issue I have with this water tank. So, after my first posts I figured out what I need to do to heat the water whenever I want to. I was just switching on the Water Heater switch whenever the hot wate was gone and the whole water was heated in about 4-5 hours.

Now all of a sudden without me changing anything, the water was being heated for only 1 hour and that was not lasting not even for 5 mins of shower (!)

A plumber came and replaced some parts (in red circle on attached photo). But the issue still persists. I'm getting very frustrated!

Anyone has any experience why this might be happening?
 

Attachments

  • Water tank.jpg
    294.2 KB · Views: 25
Nicole: The time switch you circled in red in pic 2 of #1 controls the top element which heats the upper volume of the tank. For the timer to run the Left switch marked 'Water Heater' must be on and its orange light glowing - is the orange light glowing? If it is not glowing then open up the lid of the consumer unit above and search for a circuit breaker which says 'water heater' - is the lever up or down? It needs to be up for power to the 'water heater'.

For now the timer needs to be in the 'constant ' mode which is when the small knob is in the 'I' position. If the water heater switch is on and the orange light glowing and the small knob in the I position then the top element should be on and heating up the water in the upper volume.

Did the plumber change the thermostat in the top or bottom element or both?

Now to the bottom element. Being at the bottom it will heat the full volume of water but since it is a larger volume of water than for the top element it will necessarily take longer. It should be connected to a so-called 'off peak' supply. I suspect - but need you to find out for me - that this element is turned on and off by your electricity meter - the one you put your key card into. Obviously the right hand immersion switch needs to be on ie rocker down. You may not see its orange light come on unless the time is during the off peak tariff period. There are a number of off peak tariffs on offer - some which only provide cheaper electricity over night 0000 to 0700 called Economy 7 and others which also provide some periods during the day and evening eg Economy 10. To find out whether you have an off peak tariff and which one I need you to look at your bills from your electricity supplier or to ring them up. Or you can take a photo of your bill and attach it for me to look at but do cover up your name, address and account details beforehand.

I also need photos of the full electricity board on the right side wall of the water tank cupboard and one of your prepayment meter - cover up any account details. Also lift up the lid of the consumer unit and take a picture of the rows of switches (circuit breakers) and what is written underneath them.

The advice in the first two paragraphs I hope will provide you with some hot water albeit only half a tank's worth until we sort out the bottom element.
 
Last edited:
Yes, the orange light of the “Water Heater” switch is glowing. Also, it’s been a few months now that I have the timer to the permanent position and never changed that again.

The plumber changed the thermostat in both the top and bottom elements.

I don’t have anything in that cupboard where the tank is that says “Off peak”. Also, back in October I changed to a credit meter.

About the righthand side switch that says “Night immersion” you are right. I never see the orange light on.

As for the economy 7, I had called British Gas and they told me I’m not on Economy 7. I’m on the variable tariff.

I called OSO and I’ve sent them photos, the replacements that were done by the plumber and what the issue is and they told me that probably the immersion heater is faulty. Could that be right?

The plumber told me that he has ordered new parts for the cylinder, hasn’t told me what these parts are.

Photo attached of the consumer unit.

Thanks for your help!
 

Attachments

  • 20230318_114531 (1).jpg
    279.4 KB · Views: 20
Thank. Are you able to send me a picture of your meter and the items around it please?

The reason I want this picture is I suspect the electricity supply for your night immersion heater is or has been controlled by the meter. To take advantage of cheap overnight electricity ie E7 you need to sign up for this tariff and you are not it seems. So your meter will not turn on the bottom element on during the E7 cheap rate period.

There are a number of ways to control an immersion heater to use E7 which is why I need the picture(s).
 
Last edited:
The plumber changed the thermostat in both the top and bottom elements.
It may be the thermostat is set a little too low in temperature but we can come to that later.
I don’t have anything in that cupboard where the tank is that says “Off peak”. Also, back in October I changed to a credit meter.
Please send me a picture of meter and what is around it.
About the righthand side switch that says “Night immersion” you are right. I never see the orange light on.
When/if you get up in the night betwee 0000 and 0700 could you take a look at the right switch for the Night Immersion and see if the orange light is glowing? Don't do it exactly at 0000 or 0700 'cos the switch on and offs can be staggered.
As for the economy 7, I had called British Gas and they told me I’m not on Economy 7. I’m on the variable tariff.
I am on a variable tariff but still have E7. Just look at your latest bill since the new credit meter and see if you can see day and night rates.
I called OSO and I’ve sent them photos, the replacements that were done by the plumber and what the issue is and they told me that probably the immersion heater is faulty. Could that be right?
Yes it could be the bottom element has failed. But I cannot say anymore just now. You are getting hot water from the top element still?
The plumber told me that he has ordered new parts for the cylinder, hasn’t told me what these parts are.

Photo attached of the consumer unit.

Thanks for your help!
:)
 
Last edited:
I wouldn't mind sending a pic of the meter reading, but where can I find this? Would it be in a communal area in the building or in the cupboard where the water tank is?

Yes, I'm only getting hot water from the top element.

I looked at the latest bill and there are no day or night charges. Attached the latest bill for your info if that helps.
 

Attachments

  • Leccy.jpg
    50.9 KB · Views: 21
I would expect it to be where your previous prepayment by money key/token was located.

And not far away at all from the grey thing with 100A written on the side nor far from your consumer unit. Can you ask neighbour where their one is?

Your bill shows you are on a single rate tariff of 38p a kiloWatthour with no cheaper rate periods at night or during the day.

Do you have electric space heating?
 
Photo attached of the meter. Does this help?

Can I ask British Gas to add me to the E7? or how is this done?

Do you have electric space heating?
Yup, I have electric heaters to heat the rooms if that's the question. I don't have gas at all in the flat.
 

Attachments

  • Meter.jpg
    636.9 KB · Views: 19
Nicole - I think any further advice from me will have to await the repair by the plumber using the parts on order: do you have a return date?

Once this is done you need to confirm with him which element he has left connected to the timer which is to the left of the Delta Dore controller labelled 'Heating'.

Then we need to have another discussion including changing your tariff to one which includes periods of cheap electricity if your usage of space and water heating suits those on offer/available to you.

Is your flat similar to others in the block? If your flat's design for water and space heating is repeated in neighbouring flats it would be helpful to see some pictures of their electrical equipment ie the sort of pictures you have provided me already.

Is this fine with you for now? Do say if not.
 
Well, I'm confused to be honest I worry if the plumber makes things worse and end up without hot water at all.

How is it possible that after he changed the parts it worked for a day and then the next day nothing? That's what I don't understand. What could that mean?

I just feel that if I don't understand a little bit what is happening then I don't know if I can understand whether he knows what he is doing or not.

Could it be a problem with the switches and not the water tank at all?
 
Well, I'm confused to be honest I worry if the plumber makes things worse and end up without hot water at all.

How is it possible that after he changed the parts it worked for a day and then the next day nothing? That's what I don't understand. What could that mean?

I just feel that if I don't understand a little bit what is happening then I don't know if I can understand whether he knows what he is doing or not.

Could it be a problem with the switches and not the water tank at all?

While anything is possible (almost), I'd advise continuing with the investigative process started by @marconi

He seems to be working methodically through the possibilities and providing the information requested will result in a thorough analysis of the problem. Granted this may not be as fast as a visit from a local spark, but his help here isn't being charged at an hourly rate.
 
Nicole: Thank you for your last post. You are clearly exasperated and who wouldn't be. I'll explain what I think is the situation at the moment.

1. Your flat relies on electricity for space and water heating. To be most economic you need to be on a dual rate electricity tariff such as Economy 7 or Economy 10. These provide periods of cheaper rate electricity. Time switches are used to turn the space heating and water heating on and off to utilise the cheaper rate periods. At the moment you do not have a dual rate tariff. I believe you 'lost' a dual rate tariff when you swapped from the pre-payment meter to a credit meter with British Gas.

2. Your hot water tank has two elements, the bottom one to use cheaper rate electricity and the top one as a boost using whatever tariff is operating when it is on. What I cannot know now is whether the time switch to the left of the Delta Dore controller was for the bottom element to switch it on during cheap rate; the top element being then simply controlled manually by the left hand 'Water Heater' switch - you'd have to remember to turn it on and off.

3. I reckon though that the time switch to the left of the Delta Dore is for the top element as it is used now. The bottom element was then being switched on and off for the cheap rate by the old prepayment meter. There is a hint to this set up by the thinner brown grey vertical wire going into the brown plastic box with 'PROTEUS' written on it. I believe it previously went into your old prepayment meter. But since your change to a credit meter, which does not have an output which switches on and off during cheap rate, it has been connected to the brown box which now provides a permanently on supply for the bottom element. The bottom element is now only being controlled manually by the right hand 'Night Immersion Heater' switch. Thus, the change from prepayment to credit meter has resulted in no time control of the bottom element meaning it has been on constantly albeit regulated in temperature by its thermostat. Meter change men/women are not obliged to ensure any downstream effects of the meter change are attended to. So since your meter change I believe - perhaps you can confirm from experience - the top element has been controlled on/off by the time switch left of the Delta Dora and the bottom element has been on permanently if its switch is on.

4. Now, I may not have the full history of this panel correct because one can see a square white plastic blank fitting bottom left below the 'Immersion Heater' switch. It may have once had a square timer here which looks like this:

Electrisaver Immersion Heater Booster - https://www.tlc-direct.co.uk/Main_Index/Water_Heating_Index/Immersion_Heater_Timers_2/index.html

or this

24 Hour GP/Immersion Heater Timeswitch - Flush/Surface | Timeguard (NTT01) - https://www.tlc-direct.co.uk/Products/SMNTT01.html

These would control the top element. The timer to the left of the Delta Dora would then do the bottom element.

5. With me so far? ;-)

6. Good. You told me that you had never seen the right hand 'Night Immersion Heater' switch orange light on when the switch is on. This is odd because now, since the credit meter, it has a permanent supply all day long via the red switch and the 16A circuit breaker on the far right of the consumer unit and it is clear from the photo that these two switches are both on - they in the up position. This indicates that the supply has been disconnected somewhere at or before the 'Night Immersion Heater' switch. This begs the question why would someone do this?

7. I suspect - cannot know for certain - the plumber has disconnected the supply to the bottom element because he found it defective. The spare on order would be the replacement element. He may have temporarily connected the top element to the timer to the left of the Delta Dora to the top element or it may have been always so.

8. I cannot investigate the disconnected supply because it would require live electrical equipment to be opened up. This is why I said we must wait for the plumber to return and finish his work and I asked you to clarify with him how the top and bottom elements have been connected.

9. When we have two working elements we can discuss dual rate tariffs which depending on your lifestyle and electricity use profile may be more economical. You could have a read of these in the meantime from which you will learn about E7 and E10 and some other tariffs.

What is an Economy 7 meter? | Understanding Economy 7 - https://www.uswitch.com/gas-electricity/guides/economy-7/

What is Economy 10? A complete guide to Economy 10 meters and tariffs - https://www.uswitch.com/gas-electricity/guides/economy-10/

7 facts about Economy 7 meters, tariff and times - https://www.edfenergy.com/energywise/all-you-need-know-about-economy-7

10. I hope this provides some clarification. The most important thing to say is that as a tenant your landlord is responsible for fixing this problem in a timely fashion using qualified contractors. It is reasonable to wait say a week maybe two weeks at most for spare parts but any longer it is not. How long ago since the plumber visited?

11. I have sent you my mobile number if you want to call me. If I don't answer straight away leave a message or send me a text/whatsapp.

PS: Re your #6 - it looks like the top element white wire goes into the timer and the bottom element white wire goes into the white plastic trunking - is this still the case?
 
Last edited:

Reply to OSO hotwater boiler_Issue heating the water in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Calling all electrical professionals / boiler tradesmen -WE NEED YOUR HELP! Every so often (twice in the last two days) when running the hot...
Replies
15
Views
347
Hi I'm in a bit of a pickle trying to set up my hot water and central heating systems. Got a gas boiler with a pressure tank and a motor...
Replies
7
Views
852
Good Afternoon All, I moved into a flat around 2 months ago. A few times only (maybe four times in the two months) I've turned on the kitchen...
Replies
14
Views
1K
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
441
Good afternoon chaps, I have an Alpha E-Tec 33 combi boiler (with Google Nest 3rd Gen thermostat) that occasionally fails to put out hot water...
Replies
10
Views
956

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock