Discuss Outside lighting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
72
looking for a bit of info

went to look at a job today sorting outside lighting, the cut out is a mess. The swa are not terminated using glands and instead earth clamps round the exposed armouring. It is a tnc-s supply and am sure i have seen it some where that the end light should have a rod connected to it, although i can not find this in the regs. What i did find that reg 559.10.3.4 requirea a mimimum copper equivilent conductor not less than 6mm. It only has a 2.5mm2 3 core and the swa works out at about 2.4mm2 something copper equivilent conductor.

Any ideas cheers:rolleyes4:
 
if the L and N conductors are 2.5mm, then the cpc need not be more than 2.5mm. IMO. the terminations need sorting though with proper glands.
 
559.10.3.4 : The Earthing conductor of a street electrical fixture shall have a minimum copper equivalent CSA of not less than the supply N conductor at that point or 6mm^ whichever is the smaller
 
when you say the cutout is a mess is is a proper street lighting cutout? these sometimes just have a brass cone on which the armoured goes over and indeed is clamped on with a pipeclamp type band
Street Lighting Cut-Outs
 
Last edited by a moderator:
jase beat me to it, while i was making a sarcastic comment on another thread. as i said in post #2, same size as L/N conductors is compliant. the 6mm comes in where the L/N conductors are >6mm
 
What i'm thinking about, is if these are pole mounted lighting units, then the metal poles may well be extraneous, being set in the ground in a concrete base, and could well need a bonding conductor linking these posts out on a PME supply...
 
cheers guys

it is small private lamposts in a car park with 2 x 70w sons. They are not glanded of and not restrained ( only thing that is holding them in place are the terminations). originaly went to change lamps and noticed it when pulling out the cut out fuse
 
What i'm thinking about, is if these are pole mounted lighting units, then the metal poles may well be extraneous, being set in the ground in a concrete base, and could well need a bonding conductor linking these posts out on a PME supply...

was thinking along the same lines. I know i have seen a bit about a rod at the end one. Not sure if its in GN8 which i dont have at hand right now. Hench why i asked you kind fellows
 
was thinking along the same lines. I know i have seen a bit about a rod at the end one. Not sure if its in GN8 which i dont have at hand right now. Hench why i asked you kind fellows


Then i would first test these poles, (you haven't confirmed or otherwise if these are pole mounted lighting?) to find out if they are extraneous or not. If they, are it would be far easier to TT these poles than to provide a bonding cable!!

EDIT ...sorry i missed the post where you confirmed they were posts ...lol!!
 
Last edited by a moderator:
was thinking along the same lines. I know i have seen a bit about a rod at the end one. Not sure if its in GN8 which i dont have at hand right now. Hench why i asked you kind fellows

It doesn't matter too much where the TT rod is installed, so long as all the posts are connected via the SWA from the post position where the Rod is connected too!! Don't forget to isolate the incoming supply SWA, as that will still be at the house PME potential...
 
Last edited by a moderator:
There does not seem to be anything specific for street furniture in the regs.

5 second disconnection time for the distribution circuit (TT or TN)

Should be RCD'd (locally)

Only (the frame etc.) needs earthing if non-sheathed cables are used or class 1 fittings are used.

having said that I only have the 'old' GN8, as I haven't got the new revised copy
 
Last edited:
There does not seem to be anything specific for street furniture in the regs.

5 second disconnection time for the distribution circuit (TT or TN)

Should be RCD'd (locally)

Only (the frame etc.) needs earthing if non-sheathed cables are used or class 1 fittings are used.

having said that I only have the 'old' GN8, as I haven't got the new revised copy

This is basically garden lighting fed from a ''domestic supply''. I don't think the section your referring too applies in this instance!! Though i may be wrong!! ..lol!!
 
Hi E54,

it comes under the heading 'highway supplies' , as far as I read it, it does not really point to any difference as whether this is private or public.

It also points to section 4.12 in GN5, where it mentions the 'anomaly' re: disconnection times up to the switchgear in each item.
 

Reply to Outside lighting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
476
Qualified electrician has installed Zappi car charger outside house. Grid incoming goes to DNO cutout then to SPD then to meter then to henley...
Replies
21
Views
5K
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock