Discuss Please help. Sockets on wooden skirting. in the The Welcome Forum area at ElectriciansForums.net

Personally I would ask the person doing the survey to produce his qualifications for making assessments on wiring matters ? At the point he then informs you he has none I would then continue with in that case I would like you to amend your report to cover the facts he is qualified to assess and also make arrangements to compensate you for undue stress and extra expenses in having the matter looked in to by people far more qualified than he is ! And if you ever hear of him doing surveys in the future that he is not qualified to do you will take further action to have him further reprimanded via the courts. Guys that know nothing about what they are doing are better leaving the job to those who do know and these guys doing home assessments some know nothing about everything and charge the earth for writing absolute rubbish ! Having said that I know of at least one sparky that bought a Megger 1730 test meter and got a demo on how to use it he took notes of all the results and these were the results he then used on every house he tested ! He is now dead and gone and too late to do anything about it but it shows you there are chancers everywhere which is why I would welcome a regulation where as you can't test your own work !!
 
Maybe a little harsh on the self employed sole trader.

It would also drive up legitimate electricians costs to the customer encouraging them to use an unqualified unskilled DIYer.
I am self employed and would back someone else testing my work anytime as if your doing it right you have nothing to fear and if everyone had to have their work tested by someone else then everyone's price would go up by the same amount sounds fair to me
 
I am self employed and would back someone else testing my work anytime as if your doing it right you have nothing to fear and if everyone had to have their work tested by someone else then everyone's price would go up by the same amount sounds fair to me
I agree anyone can come and test or inspect my work , but I don't think it would be practical for the reasons I have given.
 
I agree in principle to your idea.
It would make everyone pull there pants up a bit. Metephorically speaking. And it would improve or get rid of the registered electricians who aren't up to scratch.
But it would have to be implemented along side another policy to get the unregistered/ unskilled DIYer to keep away from electrics.
So when our prices go up due to this extra layer of testing the customer cannot go to some numpty who does no test or inspect and is charging probably a quarter I am charging.

I think it's the second policy to keep numpty' away from electrics that will be the stumbling block.

We seem to have gone off topic a bit here.
 
IMO, it is too low putting strain on the flexes, no issue with mounting on the skirting, if it was 2ft wide like most Victorian dwellings . In this scenario I would like to see it sitting on top of the skirting board.
 
Hi. I'm a currently selling my home, a Victorian Terrace house from the early 1900's.

The buyers have just had a survey completed which has highlighted a plug socket mounted on wooden skirting as a fire hazard.

We have been living here since 2013 and have had no issues, this was installed before our purchase of the house. I am keen to understand the regs and my options.

It is a double socket mounted on a plastic back box. It is not so close to the floor that the flex from a plug is severely bent.

I would be really grateful for some advice. I believe it's only because this is a '3' on the homebuyers survey. Can someone tell me when the regs came in and if they relate to installations prior.

Thanks all.
 
It does seem abit OTT for that catergory alot of older properties especially of that era had pvc boxed sockets fixed to wooden skirting boards if the buyer wants to upgrade the sockets and consumer board i dont see it being a problem
 

Reply to Please help. Sockets on wooden skirting. in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
756
Hi all and please forgive me if this has been asked many times before, I'm trying to purchase and get installed by one of the national...
Replies
0
Views
2K
Hi all, Just moved into a house and typically now finding a fair few issues. Hoping to have an EICR done at some point, would've done this before...
Replies
3
Views
2K
Not come across this before, so would like some help, please. I went to install smokes and heat alarm (to new Scottish regs) in a fairly modern...
Replies
2
Views
1K
Long time lurker so this may be my first question. I am a qualified electrical engineer, but in aeronautics not domestic installations, and I may...
Replies
21
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock