Rayserb

DIY
Reaction score
0
Power connection of unknown source (prob socket spur) connected to outdoor light. Can i disconnect the existing light. Connect up RCD plug and then connect a switch to control a new outdoor light like picScreenshot_20210909-160824_Outlook.jpg
 
If it is spurred from a ring final circuit then no.
 
It needs to be established If the internal socket is connected from a 30/32A ring final circuit and that it is part of the ring final and not a spur itself. If it is part of the ring final then it needs a fused spur prior to the new socket and light. If your consumer unit has 30ma rcd protection for this circuit then there is no need for the outside socket to be an rcd socket.
 
It needs to be established If the internal socket is connected from a 30/32A ring final circuit and that it is part of the ring final and not a spur itself. If it is part of the ring final then it needs a fused spur prior to the new socket and light. If your consumer unit has 30ma rcd protection for this circuit then there is no need for the outside socket to be an rcd socket.
Thanks for that
 

Reply to Power connection of unknown source connected to outdoor light. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all, I am planning to install wall lights such as these ones (LAP Bronx Outdoor Up & Down Wall Light Black - Screwfix -...
Replies
5
Views
686
We have an outdoor socket that is hard wired into the ground floor power circuit and protected with an rcd in the consumer unit. I now plan to add...
Replies
17
Views
3K
Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Replies
1
Views
884
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
537
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
450

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock