Discuss problem with making circuits in the UK Electrical Forum area at ElectriciansForums.net

G

Gktssm

Hi,
I was wondering if someone could help me. I have an assignment to do and i have no idea how to make circuit for the 16A TP_N, welding equipments, door control. I have attached a pic so plz if anyone can help.

Thanks.

And What about the wiring on the left side for lighting and radial? Any help would be much appreciated.
 

Attachments

  • IMG_20140322_194823.jpg
    121.8 KB · Views: 199
wow ! nice waste of cable on the left side lights lol ;-)

well door control & welding will be dedicated radials , so decide what sort of cable you want to use , work out the loading amps , then measure the length of each circuit.
and from there you can do the full cable calc to confirm the correct size csa.

that looks suspiciously like a C&G drawing ??............. ;-)
 
wow ! nice waste of cable on the left side lights lol ;-)

well door control & welding will be dedicated radials , so decide what sort of cable you want to use , work out the loading amps , then measure the length of each circuit.
and from there you can do the full cable calc to confirm the correct size csa.

that looks suspiciously like a C&G drawing ??............. ;-)

2396 project?
 
What exactly are you struggling with?
Might be better if you posted up your thoughts and we can help from there
I am confused about this 16A TPN (switched fuse disconnecors) inside the worshop all around the wall and 230v 4kw and 3kw (welding equipment). Shall i connect them in one circuit or what to do?
 
welding equip will need a seperate circuit for each unit.
welding equip will need type D mcbs
welding equip is best wired in swa if its in an industrial environment........


there , i've shown unprecedented mercy and given you a head start.........
 
welding equip will need a seperate circuit for each unit.
welding equip will need type D mcbs
welding equip is best wired in swa if its in an industrial environment........


there , i've shown unprecedented mercy and given you a head start.........

Thanks
 
welding equip will need a seperate circuit for each unit.
welding equip will need type D mcbs
welding equip is best wired in swa if its in an industrial environment........

there , i've shown unprecedented mercy and given you a head start.........


Not necessarily so, You could install a circuit with the provision of say 3 welding outlets, The outlets providing convenient means of connection at different locations/positions around th premises. eg, ..A single welding machine, with a circuit that can supply that welding machine at several locations...


I would think heavy gauge screwed metal conduit to be far superior to SWA cable in an industrial environment myself!!
 
Im guessing this hasn't been dropped in your lap without preparation, you teaching and notes and books you use will have all the relevant info' within them, as we are not on your course it may be the fact we can see various ways of doing this where as your course is looking for a specific design related to your tutoring, if you waltz in with a set-up beyond what you have been taught then alarm bells may ring that you haven't done the work yourself.

I understand it can be confusing but your notes and books are your best source here, what do they say about designing such a set up?
 
Im guessing this hasn't been dropped in your lap without preparation, you teaching and notes and books you use will have all the relevant info' within them, as we are not on your course it may be the fact we can see various ways of doing this where as your course is looking for a specific design related to your tutoring, if you waltz in with a set-up beyond what you have been taught then alarm bells may ring that you haven't done the work yourself.

I understand it can be confusing but your notes and books are your best source here, what do they say about designing such a set up?
Could find any info thats why needed help from the big Boys.
 

Reply to problem with making circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
232
Wonder if anyone can help out, my experience in heating is minimal. So house I was working in had a circuit for the water heater, which went to a...
Replies
4
Views
334
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
716
Hi All, Would be grateful for some advice. Would like to add an additional light (Undercabinet 8W LED Batten light) to a two-way light switch...
Replies
7
Views
620
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
846

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock