Who installed the sub main and the lighting then? Where has he gone? The on site guide gives diversity calcs on heating appliance's. client may be ppaying for it but it will be you who is being sued when the system keeps overloading. If you are going to stand by your loading calcs you should make sure you have professional indemnity insurance. this is why engineers get involved.
 
They Landlord had their own electrician carcass out the high lighting and install the submain which isn't connected or tested from what I have seen. Only reason I know the loading fotr the lights is that I counted and Calculated it first and its all one bank as well.

Not sure why there was no consultation about the requirements for the supply though its rather odd in my opinion

I have the OSG out in front of me water heater diversity is only applied once there are 3 instantaneous heaters in the installation there are only going to be two and the third is an undersink unit with storage so all are 100% of f.l. regardless of being domestic or commercial from the way I read it.
 
you dont need a chartered engineer for a modest commercial extension mark.
this is straightforward load assesments and planning that any competent designer \ installer could undertake.
as for getting sued from overload ? (if it ever happened )
i'd blame the owner as it was he whom specified the dno supply ;-)
 
I have the OSG out in front of me water heater diversity is only applied once there are 3 instantaneous heaters in the installation there are only going to be two and the third is an undersink unit with storage so all are 100% of f.l. regardless of being domestic or commercial from the way I read it.

Agreed. It wasn't the water heating I was concerned about, I thought your cooking appliances calcs were wrong.
 
you dont need a chartered engineer for a modest commercial extension mark.
this is straightforward load assesments and planning that any competent designer \ installer could undertake.
as for getting sued from overload ? (if it ever happened )
i'd blame the owner as it was he whom specified the dno supply ;-)

Biff, I totally agree. But Jon has said he is not confident with his calcs and therefore could consider whether he wants to stand by them. And I agree with both of you, it seems very strange that someone has installed circuits already but has not had consultation and has now vacated the site. Who is going to sign this work off and connect it?
 
Domestic cooker installation says 10A +30% f.l. of connected cooking appliances in excess of 10A gives 18A if i got it right.

Commerical says 100% of f.l. of largest appliance and 75% of f.l of remaining appliances which is where the 30A comes from
 
Its not that I'm uncertain of my calcs as such its just that I wanted to make sure that I was on the same page as everyone else and that I hadn't ballsed up my interpretation of the OSG if you get where I am going with this.

First time doing any commercial work under my own steam I've done plenty before thats been worked out before hand by someone else.

Rest assured it will not be me testing what has gone in already I will not put my name to it period, I am not putting my name to the installation of the board either only going on the circuits I put into place!
 
Oh dear god, are you really trying to make those max demand and diversity formulas quoted in the BGB work?? Best of luck to you if you are!! They are totally useless (except for the domestic cooker formula) except maybe for make believe C&G questions!! Unfortunately for you, it's takes many years of experience to assess by calculation only, accurate results...
 
Oh dear god, are you really trying to make those max demand and diversity formulas quoted in the BGB work?? Best of luck to you if you are!! They are totally useless (except for the domestic cooker formula) except maybe for make believe C&G questions!! Unfortunately for you, it's takes many years of experience to assess by calculation only, accurate results...

Which is why I said, 'this is why engineers get involved'
 

Reply to Problems with Maximum Demand figure in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hi all, I have a regular client who has asked for a battery back up system to be installed at their home. They live in a rural location on a...
Replies
2
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
522
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
This isn't sitting right with me. So if I rock up at a house with a 60A suppliers fuse, it has a dear old Wylex with 1 RFC 30A (no diversity) 1...
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock