Search the forum,

Discuss Programmer close to sink in the UK Electrical Forum area at ElectriciansForums.net

S

stratplus

Thoughts on this?

dajaju6e.jpg
 
Electrical apperateus segregated from non electrical services.! So you'd put it there murd..?

It's segregated from the other services, it's not a cable strapped to a gas pipe or anything like that is it?

Nobody has said they would install it like that themselves, just that you'd be hard pressed to find a reason to condemn it.
 
Not a place I would fit it however the guideline is 300mm horizontally from the drain point. Note the word guideline it's not a regulation.
 
BS 7671 does not specify any minimum distance for socket-outlets to be from a sink. However, regulation 512.2.1 requires external influences to be considered when selecting equipment for a particular location. Accessories used in domestic installations are not designed to be splashed and therefore not suitable for installation close to a sink or draining board. For this reason, it is recommended that socket-outlets and other accessories should be located at least 300 mm, measured horizontally, from a sink or draining board, where they are less likely to get splashed.

Straight from the ECA website.

Doesn't say guideline but does say recommendation davesparks will this pass?!
 
..... Straight from the ECA website. Doesn't say guideline but does say recommendation ......

Also 300mm is guidance in the likes of the IET publication "electricians guide to the building regs".

The trouble with any form of guidance/recommendation (which is effectively what BS7671 does) is that you don't need to follow it and provided nothing goes wrong all is tickty boot.

However, once something goes wrong and you are in a court of law then you will have to justify technically why you didn't follow the recommendations given by the authoritative electrical bodies (IET, ECA etc ....). Which is a big ask for a humble tradesman when the electrical bodies wheel out their 'experts' to give evidence as to why it should have been followed.

For anyone who has not been there its a harrowing experience to see a colleague shot to pieces when an 'expert witness' gives his view to a court of law .....
 
Yes, when the sink was put in doesn't effect the EICR code, you judge it as you see it when inspecting and decide if its safe or not.

But if you were the 'electrician' who installed it before the sink was put there then there shouldn't be any comeback on you for bad workmanship ........ if you can prove that was the case. Depending on what legislation you are prosecuted under you can be assumed guilty until you prove yourself innocent.

However, there would have to have been a pretty nasty incident/accident for any prosecution to be forthcoming!!
 
That's building regs not BS7671 regs

The problem is that regs such as 512.2.1 requires that the effect of external influences be considered on equipment being used. Guidance then in support of this suggest that within 300mm is considered unsuitable.

Ultimately you as the inspector have to decided if water and electricity can mix in this instance and be considered safe for continued use ...... personally Id be covering my ar*e and saying its not and coding appropriately!!
 

Reply to Programmer close to sink in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
670
Hi Guys Changing my heating/water programmer and im stuck on the wiring ive gone from a danfoss to a Drayton and the wiring description is...
Replies
5
Views
1K
Hi all @ef.net, I'm a newbie to the forum; this is my first post. The Danfoss FP715si programmer that had been in use for about 8-9 years began...
Replies
22
Views
1K
Anyone tell me where to connect the two wires that switch the boiler on via the programmer and the 2 wires that call for heat on the ufh control...
Replies
1
Views
310
Why is it that so many timers, programmable thermostats (and the like) are still manufactured without the ability to automatically change the time...
Replies
9
Views
438

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock