trogg

Hello all
As a property developer I quite often have to replace sockets and switches which I believe I'm allowed to do ? However I'm not 100% sure what I am allowed to work on.
So, 2 questions,
What can I legally work on, and what courses do you recommend ?
Thanks
 
Re: Property developer, What electical work can I do ? and what course should I go on

You are legally allowed to replace any accessories in all rooms, except bathroom and kitchen. You are also not allowed to carry out any external electrical work.
 
Re: Property developer, What electical work can I do ? and what course should I go on

Thanks Adam for your reply,
The things I'd like to be able to do are, removing and replacing things like a shower or an extractor fan etc when re-plastering or tiling, but like you said, I'm not allowed to do this at the moment.
I believe there is a 17th edition course, what's that all about ? will it be any good for me ?
 
Re: Property developer, What electical work can I do ? and what course should I go on

If you are not "competent" to carry out electrical work then you should not be doing any.
If you are, then you can do anything which your training has prepared you for, though you will need to carry out testing for everything except "like-for-like" replacements (and even some of this work needs testing).
If you search the forum or internet for "part P", you will see what needs notifying to LBC.
As for courses.... Enrol on an apprenticeship, or else leave electrical work to electricians :)
 
Re: Property developer, What electical work can I do ? and what course should I go on

I believe there is a 17th edition course, what's that all about ? will it be any good for me ?

The 17th edition course is for experienced electricians to "top up" their knowledge of the latest regulations. It is not an electrical course as such (being only a few days long).
 
Re: Property developer, What electical work can I do ? and what course should I go on

Like for like replacements are non-notifiable regardless of what location they are in however, the fact that you are asking about regs and courses tells me that the "Default" advice should kick in here mate. Get a qualified electrician in
There is more to electrical work than just connecting up.
 
Re: Property developer, What electical work can I do ? and what course should I go on

For some reason my posts keep getting denied, not sure what I'm doing wrong
 
Re: Property developer, What electical work can I do ? and what course should I go on

I do use electricians, but have a lot of trouble getting someone in to do the smaller jobs, most of the properties require complete renovation and getting electricians in is no problem.
 
Re: Property developer, What electical work can I do ? and what course should I go on

There's a lot of spamming going on on the forum just now and maybe there's stuff in your posts that's falling foul of the filters, maybe that's why some of your posts are going walkabout.
A lot of guys love the daft little jobs that only need a quick fix, myself included, ok it might cost you a bit but it may be worth your while to get on really good terms with one of your regular sparks. Try posting up your rough location
 
Re: Property developer, What electical work can I do ? and what course should I go on

Thanks trev, I live in Birmingham, the other side of the city to Adam ( above) I have Electricians I can use here but most of the properties are some distance away i.e. the last properties I've been to look at were in South Wales and Stoke.
The Stoke property needs the bathroom replastering/tiling which would involve removing and replacing the shower, a job I'd like to legally do but if you're saying I need to be a fully qualified electrician to do this (no short course for someone like me) then I'll just carry on phoning around till I find someone to do it for me.
 
Re: Property developer, What electical work can I do ? and what course should I go on

One thing I've noticed is that most of the electricians I've used for the smaller jobs have been quite old, what am I going to do in a few years time when they've all retired ?

:)
 
Re: Property developer, What electical work can I do ? and what course should I go on

One thing I've noticed is that most of the electricians I've used for the smaller jobs have been quite old, what am I going to do in a few years time when they've all retired ?

:)
Find younger ones ;)

I know there will be huge debate now, but even when replacing accessories you should (in my opinion) as a minimum be taking a Zs reading, just to cover yourself. I doubt that trogg has the equipment to do so or the expertise to interpret the readings?
 
Re: Property developer, What electical work can I do ? and what course should I go on

Find younger ones ;)

I know there will be huge debate now, but even when replacing accessories you should (in my opinion) as a minimum be taking a Zs reading, just to cover yourself. I doubt that trogg has the equipment to do so or the expertise to interpret the readings?

I agree. Say you remove the shower, tile and replace it.... How do you know that there is a good earth connection? How do you know what your Zs actually is? How can you check while doing the job that the cable and OCPD are actually suitable? These are the sorts of things an electrician will do, and you probably don't even realise they are doing it.
 
Re: Property developer, What electical work can I do ? and what course should I go on

I agree. Say you remove the shower, tile and replace it.... How do you know that there is a good earth connection? How do you know what your Zs actually is? How can you check while doing the job that the cable and OCPD are actually suitable? These are the sorts of things an electrician will do, and you probably don't even realise they are doing it.

I agree too, which is why I'm asking the question about courses, it looks like there are no courses suitable for my needs however some good has come out of asking the question on here, I've had a few PMs (which I can't reply to because I don't have enough posts) from people offering their services for smaller jobs :)
So in future if I need an electrician I'll just post on here :)

Thanks for your help
 
Re: Property developer, What electical work can I do ? and what course should I go on

The Stoke property needs the bathroom replastering/tiling which would involve removing and replacing the shower, a job I'd like to legally do but if you're saying I need to be a fully qualified electrician to do this
There's nothing in the law which says you NEED to be fully qualified, the legal test is of competency. As I said earlier, as this is a like for like replacement you don't have to notify it to building control but, my learned friends have pointed out you will need to prove you have a good earth connection and that the device protecting the shower will operate within the specified time. One of our moderators, Lenny, is in south Wales (I believe) not so much of a domestic spark but he knows his stuff and maybe could help you out
 
Re: Property developer, What electical work can I do ? and what course should I go on

i've p m-d you my mobile number. ring me if you're stuck any time.
 
Re: Property developer, What electical work can I do ? and what course should I go on

I agree too, which is why I'm asking the question about courses, it looks like there are no courses suitable for my needs however some good has come out of asking the question on here, I've had a few PMs (which I can't reply to because I don't have enough posts) from people offering their services for smaller jobs :)
So in future if I need an electrician I'll just post on here :)

Thanks for your help

You sound like a decent and conscientious bloke. I wish you well :)
 

Reply to Property developer, What electical work can I do ? and what course should I go on ? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
921
Hi guys. It would be really useful to run this past you and get a consensus/input from you for what would be a realistic amount to charge for an...
Replies
15
Views
2K
I'm unsure if I should be an electrician or maybe another trade is better. I have basically completed my first year of a foundation in...
Replies
9
Views
726
Guidance please - C&G L3 electrical installation - Hotel extension project Hi folks, I am fairly new to this forum but it looks like the...
Replies
1
Views
449
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock