Discuss RCD for Stables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

sako

Hi all,what RCD should be used in a stable.Currently theres an DP isolator switch but my spark says this needs replacing with a 30mA RCD is this correct?

TIA
 
don't take much to drop a nag. RCD deffo.
 
Im no spark so assumming 30mA is less than 300mA?


Yes...the socket MUST be on a 30ma RCD....the lights can be on a 300ma RCD....but TBH I would prefer to put all the circuits in a stables on 30ma RCD's. If you install a 30ma RCD main switch and that trips you will lose all power,although there are only two circuits,it may be better to leave the DP main switch and install a separate 30ma RCBO for each circuit.
 
Last edited by a moderator:
and watch how and where you bury the cable. should i shout it out, nay, i'll go hoarse
 
I was told that the horse has a lower dangerous voltage threshold, maybe as low as 25V.
Is it the metal horse shoes?
The front to back legs can't be much wider apart than a bull/cow.
Can anybody confirm this and is it stated anywhere?
If so is a 10mA RCD safer?
 

Reply to RCD for Stables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
328
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
764
Surely if you fit an RCBO on each circuit, an RCD is not required? Of course, a DP Main switch would be to cut all power, but like I ask, is the...
Replies
3
Views
1K
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
472

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock