Discuss reference method D in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
57
hi everyone

quick question reguarding ref method D (cables in ground/or in ducting in ground)
i can find no figures or derating factor in the OSG. can anyone help me out with either the derating factor, or the current carrying capactity for 6mm 3core SWA installed using ref method D

many thanks
 
SWA run underground, as long as it,s not more than about 2ft. deep needs no derating factor applied. IMO.
 
both as far as i know. it's because the ground temp. is usually around 10-12 deg.C.
 
single phase 46A, three phase 38A ref method D, table 4D4A of BS7671 would be my 2Ps worth :)

edit ; that is at 20C so at 15c the CCC could be x1.05
 
Last edited by a moderator:
The generally accepted depth for cables direct buried and cables buried in duct is 600mm to 650mm. Over 700mm then derating starts to rear it's ugly head... lol!!!
 

Reply to reference method D in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
917
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
457
Hi Everyone, New to the forum but hoping I can find a little help with my restoration project... I am adding a secondary wiring "system" to my...
Replies
14
Views
904
good evening all, If I have an existing 10mm T+E from the CU to the rear of the house external ending in a junction box on the wall already in...
Replies
5
Views
2K
Hi, I am a mechanical engineer tasked with some electrical engineering scope of work and not sure where to look for information on the...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock