Hi all,

DIYer here. My garage has a double socket fed by 4mm2 twin and earth connected to the same circuit breaker has the ring main for the sockets upstairs in the house. The MCB is a B32.

Is the feed in the garage considered a spur from the ring main or is it a separate radial circuit which happens to be on the same MCB? Ideally I'd like to add more sockets to the circuit in the garage (using 4mm2) but is this safe or allowed?

Thanks.
 
It would be considered a spur and being 4.0 its method of installation would dictate whether it could carry 32A and be added to. Spurred points from ring final circuits are normally limited as to the number of points which can be served but the 4.0 clouds that a bit. It sounds like the garage socket has been a later addition and connected to the existing ring final circuit and if the existing circuit is wired using 2.5/2.5 conductors it is not ideal to have differing sizes at the same protective device, are there spare ways in your consumer unit.
 
If the 4mm2 is on the same circuit breaker as the RFC then it is a Spur, as for adding more sockets to the 4mm2you would need to swap the double socket for a Fused spur unit and add sockets from that spur unit, remember the extra sockets will be limited to 13Amps governed by the fuse in the spur unit.
Another method would be to take the 4mm2 to a seperate CB (providing there is one) and form a 32 Amp Radial to your Garage (assuming it's an atatched Garage), the proviso being is that your Garage would need RCD protection, if the garage is a standalone then a different set of rules apply.
 
The question as to whether this 4.0 can take 32A is down to its installation method. The spur is somewhat unconventional as it stands.
 
The question as to whether this 4.0 can take 32A is down to its installation method. The spur is somewhat unconventional as it stands.

The 4.0 is clipped along a roof joist in the garage, exposed to the air, no insulation etc. The consumer unit is actually in the garage, but there is no space for additional circuits.

We've only been in the house a few months so trying to understand what work has been done previously.
 
The 4.0 is clipped along a roof joist in the garage, exposed to the air, no insulation etc. The consumer unit is actually in the garage, but there is no space for additional circuits.

We've only been in the house a few months so trying to understand what work has been done previously.
Theoretically you could add to it but the best course is to connect to its own protective device but this is obviously not possible.
 
New posts

Reply to Ring spurred at origin? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
781
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
Replies
3
Views
256
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
308
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
904

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock