Discuss Shower supply, ever needed additional earth cable. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Spoon

-
Mentor
Esteemed
Arms
Reaction score
7,235
This may be one for the older members on here.
Got chatting with a mate about a general supplies to showers.
At the moment you just supply the correct size cable, (usually 10mm for a new circuit) to a shower.
Was there ever a requirement/regulation to add an additional earth cable along with the power cable? Thinking old regs...
 
In the distant past I believe there was a need to add an separate earth cable, don't know the reg number or even if there was one,
 
Last edited:
In the distant past I believe there was a need to add an separate earth cable, don't know the reg number or even if there was one, I'm not a Domestic Electrician though.

Neither am I. I'm just curious about it.
It sounds like it may have been a thing when the domestic people had to earth everything metal in the house...
 
Not a separate earth as such in the 16th as I remember , but if the supply pipe was copper (conductive) it would be part of the equipotential bonding , as would all the other extraneous metal parts , including the radiator.
There is still a requirement in the latest regs unless certain conditions are met.
 
In the 16th we had a 4mm earth cable connecting to all earth terminals of the circuits serving the location in a bathroom such as the shower then to the light and then down to the extraneous pipe work under the basin, radiator etc
Looked Gorgeous darling!

Then additional protection by an rcd made my life so much easier.

I think it was the 15th when they bonded every piece of metal they could find but I’m far too young to have ever been involved with anything earlier than the 16th:cool:

Westy is your 15th edition guru on here , still reads the books I think
 
Last edited:
It is not likely the cpc was inadequate the only time this may apply was when 2.5 cables had 1.0 cpcs on BS3036 30A fuses.
 
was in 16th, all electrical equipment in bathroom supplementary bonded to each other like spaghetti. ( except the metal windows and bog flush. these were the preserve of D.W. cock something.
 

Reply to Shower supply, ever needed additional earth cable. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
825
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
494
I've been told I need to upgrade the main earth bonding to 16mm. The consumer unit is on the wall adjacent to the externally mounted incoming...
Replies
30
Views
4K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
892

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock