Discuss Smart meter install assessment failed. in the UK Electrical Forum area at ElectriciansForums.net

...Only two comments... The replacement of tails,is made all the easier,because you have a nice picture of the pre-cut seal....
Other point,is why on earth do you want Smart meters? :)
 
...Only two comments... The replacement of tails,is made all the easier,because you have a nice picture of the pre-cut seal....
Other point,is why on earth do you want Smart meters? :)

It would interest me to know the reason why:confused:

"Asking" to have a smart meter installed ?:eek:
 
Dump the Henley block and run new tails in direct.
 
It's about time they pointed out that non-sheathed cables outside of containment or an enclosure is lacking mechanical protection and is unsafe and prohibited. Not a jobsworth in my eyes.
 
No he made a valid point but why not just get on with the job and rectify the issue at the same time, just for the sake of 10 more minutes.
 
No he made a valid point but why not just get on with the job and rectify the issue at the same time, just for the sake of 10 more minutes.
As suggested by others, probably an issue of liability. His employer probably does not wish to get involved with customers' wiring.
 
No he made a valid point but why not just get on with the job and rectify the issue at the same time, just for the sake of 10 more minutes.

I would imagine it would be because they are not qualified or insured to do the job, they probably don't have the necessary tools to do it correctly either.
Plus it could of course snowball into a much bigger job, at what point should they stop and advise calling an electrician?
 
Yes fair enough, it's just frustrating though. Just this minute had a call from a customer who's changing from oil to gas c/h and the plumber has told him that I'll need to put in an earth rod for the gas pipe ! TNCS earthing there and the gas service pipe will be plastic. The saying 'A little knowledge is dangerous' is so true.
 

Reply to Smart meter install assessment failed. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
We have a meter EDMI - ES30B fitted to our property. I understand from the fact sheet for the smart meter...
Replies
13
Views
2K
Good day readers, if any,I am an old sparky, a very old sparky. I can remember old Faraday giving us lectures Wednesday evenings at evening...
Replies
1
Views
439
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
486
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock