Discuss Solar panel rating measuring in the Electrical Engineering Chat area at ElectriciansForums.net

Reaction score
0
Few days ago, I bought a solar panel. It's rating was 6v and 450 mA. But when I measured with my multimeter, It shows around 5.25v to 5.85v and 18mA to 22mA in full sunlight. My Question is - Is measuring current around 18mA to 22mA for per hour or per second?
 
Amps (or mA) are a measurement of the flow.
they are an instantaneous measurement.

Ah or mAh are terms used to show the capacity of a battery
e.g. a 500mAh battery will provide 500mA for one hour or 250mA for2 hours
the letters are made up from

m = milli (1000th of a unit)
A = amp (a Measure of electrical current)
h = hour

i expect that the rating of your panel is
voltage rating with open circuit output (no load)
current rating with dead short of output
 
I suspect the voltage and current you mentioned in your post are the on circuit no current and short circuit no output voltage respectively. A solar panel’s purpose is to produce energy/power. Maximum power is when the panel is fully irradiated and is loaded such that the power P = maximum(Vout x I out).

Manufacturers’ normally provide details of when max power is achieved in the form of a graph of. Vout against Iout. Roughly it is normally at half Vopen and half Ishort but do check because it changes with irradiation levels.

Good solar chargers have inside ‘maximum power point tracking’ functionality or MPPT.
 
Look up ‘maximum power transfer’ theorem . What this means is that if say 200 Watts is the electrical power output of a panel 200Watts is also dissipated as heat in the panel itself assuming of course 400 Watts of solar irradiation being converted Photovoltaicaly into electricity.
 
I think Current measurements should be measured in amps, not milliamps. Milliamps are used to measure the power consumption of small electronic devices like flashlights or calculators, and discharge rates of batteries in gadgets shouldn't be taken too seriously since they'll often change significantly from day to day and even hour to hour.
 
I think Current measurements should be measured in amps, not milliamps. Milliamps are used to measure the power consumption of small electronic devices like flashlights or calculators, and discharge rates of batteries in gadgets shouldn't be taken too seriously since they'll often change significantly from day to day and even hour to hour.

Not necessarily. How much current does a 60 watt mains light bulb take? The answer is definitely in mA. (obviously nothing wrong in stating it as 0.25A either though).
 

Reply to Solar panel rating measuring in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Greetings, everyone, After dedicating over a month to researching Solar PV systems, I'm nearly ready to make a decision. I owe my progress to...
Replies
1
Views
938
Hi all. We have had 7x 400w solar panels for a number of years now on our roof which is se/nw facing end terrace. 4 on se side 3 on nw side...
Replies
0
Views
849
Hello guys, I have 10W solar panel, a 7000 mah battery and 10A charge controller. there is 7 hours of light a day i have 3W little camera which...
Replies
9
Views
1K
Could i get some thoughts pls Podpoint 7KW untethered installed 2 yrs ago, working fine with EQC mercedes. Solar panel installed 3 yrs ago. Last...
Replies
0
Views
841
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
505

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock