Morning, I was just looking for some advice on what other sparks would do for the following scenario:-

A detached Garage is going to house a 7.4kw Solar Array and around 12kw of battery storage. The supply needs to return back to the main house (cable run approx. 22m) to DNO/consumer location. Would you opt for 10mm SWA or 16mm SWA ?
 
At full whack you will have circa 1.4% for 10mm and 0.9% for 16mm VD, that will be at nominal voltage, inverter will supply slightly higher voltage. You should just be OK with 10mm unless there are extremely long and power hungry lighting circuits
 
Probably not worth it for 22m, and there may not be room in the house, but you can always do as I did and run MV dc direct from the panels on 6mm or 10mm 2-core SWA, then put the inverter next to the CU.
I've never understood PV companies' obsession with always putting the inverter/s next to the panels, then running 230Vac back to the house, often in huge and expensive cable.
 
Not sure where I remember if from but I recall there being something about SWA actually being prohibited in PV installs? Whether that was between modules/strings or the array and the consumer unit I'm not sure, might be talking out my arse though so happy to be corrected
 
Not sure where I remember if from but I recall there being something about SWA actually being prohibited in PV installs? Whether that was between modules/strings or the array and the consumer unit I'm not sure, might be talking out my arse though so happy to be corrected
Answering questions at 4.01am?? That’s dedication
 

Reply to Solar SWA cable run 10mm or 16mm in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
527
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
846
Hi All, Im quoting to install an EV charger (Dont worry - fully registered, but only been 2 weeks so i'm still picking bits up). Consumer unit...
Replies
1
Views
1K
Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock