Yes........... maybe.......SO........YES OR NO.....DOMESTIC
Discuss Spd & 18th..............,,,,,, in the UK Electrical Forum area at ElectriciansForums.net
Yes........... maybe.......SO........YES OR NO.....DOMESTIC
SO........YES OR NO.....DOMESTIC
what ? make tea ,bake a cake .Id say you have to,
The risk assessment according to 443.5 is required if protection against transient over voltage is even required for electrical installations except single dwelling units.
If not performed then the installation shall be provided with transient over voltage protection.
Regulation 443.1.1 states that this section does not specify requirements for protection against transient overvoltages due to direct lighting strokes on a structure.
Again I do not see where a type 1 is required if no LPZ is present as figure 534.1 indicates the LPZ concept
It’s definitely one for debate/guidance/clarity?
I’m sure I’ll get there in the end
What Edition of the Regs will we be on before there’s absolutley no difference in opinion & it’s completely black and white?
30th edition? In the year 2140 ?
Sorry just keeled over there just need a minute to come back roundHaving just read it all I agree with you. No lightning protection installed then no Type 1 required.
Sorry just keeled over there just need a minute to come back round
How do you decide if lightning protection is even required?
I know a risk assessment is required and is under a different British standard, but how do you evaluate if an LPZ system should be considered?
Manufacturers guides really do not help.
To be fair once you spend a bit of time reading the section on SPDs it is quite clear.
In the vast majority of domestic it would be a yes.
Can't individual pieces of kit in a domestic setting such as an expensive IT setup be individually protected ? That would be a lot more economical and simpler ?