It reads as a Type 1 will not comply at all for switching surges. Type 1 is only suitable for lightning protection.

However just because a property does not have LPZ protection does not mean it does not need protection against lightning strikes - hence the risk assessment calculation in 443.5.

So if the result of the risk assessment directs to install SPDs then a combined Type 1/2 would be what is required in small installations.

Larger installs I would install a Type 1 at the mains and then Type 2 at DBs.
 
The risk assessment according to 443.5 is required if protection against transient over voltage is even required for electrical installations except single dwelling units.
If not performed then the installation shall be provided with transient over voltage protection.
Regulation 443.1.1 states that this section does not specify requirements for protection against transient overvoltages due to direct lighting strokes on a structure.
Again I do not see where a type 1 is required if no LPZ is present as figure 534.1 indicates the LPZ concept

It’s definitely one for debate/guidance/clarity?
I’m sure I’ll get there in the endo_O
 
The risk assessment according to 443.5 is required if protection against transient over voltage is even required for electrical installations except single dwelling units.
If not performed then the installation shall be provided with transient over voltage protection.
Regulation 443.1.1 states that this section does not specify requirements for protection against transient overvoltages due to direct lighting strokes on a structure.
Again I do not see where a type 1 is required if no LPZ is present as figure 534.1 indicates the LPZ concept

It’s definitely one for debate/guidance/clarity?
I’m sure I’ll get there in the endo_O

Having just read it all I agree with you. No lightning protection installed then no Type 1 required.
 
How do you decide if lightning protection is even required?
I know a risk assessment is required and is under a different British standard, but how do you evaluate if an LPZ system should be considered?
 
th

we are been round that above ,about spd ,fit or no fit that is the question .;)
 
How do you decide if lightning protection is even required?
I know a risk assessment is required and is under a different British standard, but how do you evaluate if an LPZ system should be considered?

That would be the responsibility of the building owner to sort. We are working with a lightning company at the moment and I asked a similar question a few weeks back and they use a software package that does the RA for them. He said it is almost always required and it would literally need to be an emtpy shell for the RA to state no protection required.
 

Reply to Spd & 18th..............,,,,,, in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi got a 8 panel solar system on bungalow, changing the board to 18th edition spd board Solar feed is chased into wall so will this need a type B...
Replies
4
Views
267
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
906
Hello, I was looking at installing a SPD into an existing split load RCD BG consumer unit. In the instructions for the SPD it states that it may...
Replies
2
Views
1K
I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Replies
2
Views
558
Is there a reg anywhere that states that you have to use the same make SPD inside a consumer unit. I know there are with MCB's as they obviously...
Replies
35
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock