W

wozzit99

Hi

I'm getting confused about the use of string fuses.

In the dti guide 4 or more strings in parallel require string fuses to be used in the design of a system.

In certain sma inverters, for example the tri power tl8000 they already have string fuses built in. There are 4 d/c inputs on this inverter (input A) and 1 d/c input (Input B).

Using pv sol and the inverter above it specifies for the system to work correctly there should be 4 strings of 16 panels connected in parallel.

Do I have to connect the strings in parallel before the inverter therefore needing string fuses or do I take each set of strings back to the inverter where it sorts out the parllel conection inside and protects the strings with string fuses?

Wozzit
 
Take each string back to the inverter. The 4 inputs on input A are basically paralleled with each other in the inverter so operationally it is the same as 4 paralleled strings on one input, but with the benefit of electronic string fusing.
 
tripowers have string fuses with electronic monitoring built in
you can also fit class two arrestors for surge/overvoltage or external type 1&2 for lightning/surge/overvoltage
if you have say 4 strings connect to inverter inputs over the two mppt trackers
selecting highest number of modules per string for best inverter effciency
eg - use 4 x 1000vdc padlockable string isolators if dc cables are long

they need to be 1.1/1.25 overrated on voltage/current
or use one multi input string collection boxes / isolators with built in MC3/MC4/Sunclix connectors ( multicontact type iii or iv )
these are made from 2 to 48 strings with MC connectors incomers with MC or cable gland outgoing
class 1&2 arrestors can mount inside the isolators or multi string pv fireman switches with MC connectors with UVR for remote disconnection
quick simple tooless and plug & play


use
 

Reply to String fuses? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
475
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
Hi, I opened the electrical panel of my house because I need to connect my solar inverter to the panel and got served a spaghetti of an...
Replies
0
Views
886
I have 2 arrays on 2 SMA inverters. One is 500v single string and the other is paralleled 2 x 300v strings. I have just lost one of my arrays via...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock