Hi,
Anybody got a suggestion for the cable type to run from an isolator to industrial cooker?

Situation is:
63A 3 Pole MCB wired to 4 Pole isolator via 10mm SWA (XLPE). Cable needed is to run from isolator to fixed cooker.

It's been suggested to use 16mm H07, does that sound ok?
 
Thanks.

Looking at it isn't 10mm SY rated at 47amps for 3 phase? So I think I would need 16mm (63amps)
 
Last edited by a moderator:

Reply to Suggested cable for large cooker in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
244
Hi! DIYer here. I have an MCB running to a cooker isolator switch. The RCD connected to this set of MCBs is tripping and isolating the cooker MCB...
Replies
4
Views
778
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
581
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
516
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
914

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock