Discuss SWA 16mm 3 core cable for garden office in the DIY Electrical Advice area at ElectriciansForums.net

B

Berty

Sorry if this is not the correct wat to post my query, I am new to the site. I am not a spark but would like to tap into the skills and experise on here before I set off on the wrong course with my current spark. I am having a garden office built, it has had its own CU installed but my ex spark neighbour came round to look and has caused a row with my spark by saying he was incompetent and had done it wrong. I'm confused and don't know who to believe.

The new cu is fed from house via a henley block with its own 100amp isolator. The CU in house is on a mains fuse of 100 amp with 25 mm tails.
The issue is the cable used to the garage, it is free to air, 15 m long and swa 16mm 3 core cable. 1 of the cores has been used as earth, so my spark says its 2 core single phase system which can carry 115 amp.

The room will sometimes draw 70 to 80 amps as has an electric 9.5 kw shower, sockets and lights.

My neighbour ex spark has disagreed and says 'in his day' it would be on 25mm cable. Is my house in danger or is my spark complying with current regs?
 
Last edited by a moderator:
Hi Berty, Welcome to the forum :)

Can you just clarify for us if you are an Electrician or not, you say you are but your post comes across that you are not but actually employing a spark to do your work.

If you are not a spark it will help us to know so we can relocate the thread to the appropriate section thankyou.
 
Sorry if this is not the correct wat to post my query, I am new to the site. I am a spark but would like to tap into the skills and experise on here before I set off on the wrong course with my current spark. I am having a garden office built, it has had its own CU installed but my ex spark neighbour came round to look and has caused a row with my spark by saying he was incompetent and had done it wrong. I'm confused and don't know who to believe.

The new cu is fed from house via a henley block with its own 100amp isolator. The CU in house is on a mains fuse of 100 amp with 25 mm tails.
The issue is the cable used to the garage, it is free to air, 15 m long and swa 16mm 3 core cable. 1 of the cores has been used as earth, so my spark says its 2 core single phase system which can carry 115 amp.

The room will sometimes draw 70 to 80 amps as has an electric 9.5 kw shower, sockets and lights.

My neighbour ex spark has disagreed and says 'in his day' it would be on 25mm cable. Is my house in danger or is my spark complying with current regs?

I very much doubt that really.
 
Sorry if this is not the correct wat to post my query, I am new to the site. I am a spark but would like to tap into the skills and experise on here before I set off on the wrong course with my current spark. I am having a garden office built, it has had its own CU installed but my ex spark neighbour came round to look and has caused a row with my spark by saying he was incompetent and had done it wrong. I'm confused and don't know who to believe.

The new cu is fed from house via a henley block with its own 100amp isolator. The CU in house is on a mains fuse of 100 amp with 25 mm tails.
The issue is the cable used to the garage, it is free to air, 15 m long and swa 16mm 3 core cable. 1 of the cores has been used as earth, so my spark says its 2 core single phase system which can carry 115 amp.

The room will sometimes draw 70 to 80 amps as has an electric 9.5 kw shower, sockets and lights.

My neighbour ex spark has disagreed and says 'in his day' it would be on 25mm cable. Is my house in danger or is my spark complying with current regs?

So there is no over current protection for the sub main except the DNO fuse?

Think you should talk to the spark doing the work about the design load of the distribution circuit.
 
Last edited by a moderator:
Sorry, no I'm not an electrician. I have limited knowledge at best and would never attempt to install anything, thats what I pay you guys for as saftey is everything. My question in short is can a 16mm swa 3 core cable (1 core used as earth) carry the 100 amp load to the second consumer unit? My interferring ex-spark neighbour says it cannot and has got me doubting my spark.
 
Sorry if this is not the correct wat to post my query, I am new to the site. I am a spark but would like to tap into the skills and experise on here before I set off on the wrong course with my current spark. I am having a garden office built, it has had its own CU installed but my ex spark neighbour came round to look and has caused a row with my spark by saying he was incompetent and had done it wrong. I'm confused and don't know who to believe.
Think you should clarify the situation, its seems like another shaggy dog story to me. :thinking:

Edit: posted before reading #5.
 
Last edited:
Sorry, no I'm not an electrician. I have limited knowledge at best and would never attempt to install anything, thats what I pay you guys for as saftey is everything. My question in short is can a 16mm swa 3 core cable (1 core used as earth) carry the 100 amp load to the second consumer unit? My interferring ex-spark neighbour says it cannot and has got me doubting my spark.

Thanks for the reply, I will edit your opening post and correct it, when admin is next online you may be given DIY access and the thread relocated, this will not effect any postings already made.
 
Sorry, no I'm not an electrician. I have limited knowledge at best and would never attempt to install anything, thats what I pay you guys for as saftey is everything. My question in short is can a 16mm swa 3 core cable (1 core used as earth) carry the 100 amp load to the second consumer unit? My interferring ex-spark neighbour says it cannot and has got me doubting my spark.

Simply tell your neighbour to keep his nose out.
If you have misgivings about the design, ask your installing electrician to back up up his design choices with reference to the regulations. Any decent guy will be easily able and happy to do this. Ask your neighbour to do the same.

I would say that Murdoch's post is relevant here and I doubt that the reference method is free air, more likely clipped direct.
 
OP you will need to provide some details about the type of swa used (pvc or XLPE) and how the cable has been installed. You say 'free air' which is a reference method in BS7671, not a term a layperson would use?
 
Last edited:
OP you will need to provide some details about the type of swa used (pvc or XLPE) and how the cable has been installed. You say 'free air' which is a reference method in BS7671, not a term a layman would use?

Methinks you are getting warm.:wink:
 

Reply to SWA 16mm 3 core cable for garden office in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
522
I was the 2nd sparks taking over a garden office supply job. The first sparks had fitted 10 sq mm 3 core SWA, but it actually had brown, blue and...
Replies
5
Views
828
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
975
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
Hey, I have a shed in my garden that was built and wired up by my granddad a lonnng time ago and it currently uses 2 core/twin and earth cable...
Replies
2
Views
835

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock