Discuss SWA 2 core or 3 core? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

R

reidmaguire

I dont do a lot of external works, however, I have been asked to install some power for general lighting and powerto an outbuilding with no extraneous conductive parts 15 meters from the main board and my thoughts were;

The supply is tt, so 10mm 2 core swa from spare way in main board to CU in outbuilding - outher sheath eathed to main board only. the outbuilding will be seperate tt and rcd protected.

I have been asked why I am not using 3 core SWA, and when I say it is not required, I am starting to question this myself!!

Any though on this appreciated:)
 
Your thoughts using the 2 core are exactly the advice that was given to me by the NICEIC a couple of months ago when I posed myself with the same question and was not 100% sure myself. The reason that I was given was Parallel earth paths would be present if there is a spike at either end and also a cpc connected at both ends within the SWA.

So they said 2 core SWA with armoring connected at mains distribution end and divorced at new DB, then an earth spike at the new DB with the obvious RCD protection.

Hope this helps. ;)
 
I dont do a lot of external works, however, I have been asked to install some power for general lighting and powerto an outbuilding with no extraneous conductive parts 15 meters from the main board and my thoughts were;

The supply is tt, so 10mm 2 core swa from spare way in main board to CU in outbuilding - outher sheath eathed to main board only. the outbuilding will be seperate tt and rcd protected.

I have been asked why I am not using 3 core SWA, and when I say it is not required, I am starting to question this myself!!

Any though on this appreciated:)


Spot on.;)
 
I've never really understood why you cant use the earth from the main building:confused: (not saying you can't, just that I've never had it explained properly)
Can anyone give a practical explanation please?
 
Last edited by a moderator:
So could you still used a 3 core in this situation what comes to mind is if the armoured was damaged in anyway some time ago i came across a job were a 2 core cable had been pulled out of the gland hence no earth
 
I've never really understood why you cant use the earth from the main building:confused: (not saying you can, just that I've never had it explained properly)
Can anyone give a practical explanation please?

To my knowledge, something to do with any extraneous stuff in the out-building being at a different potential to that in the main building, hence the need for a seperate earth.....I think...:confused:
 
Last edited by a moderator:
So could you still used a 3 core in this situation what comes to mind is if the armoured was damaged in anyway some time ago i came across a job were a 2 core cable had been pulled out of the gland hence no earth

I think the point is that you DONT WANT an earth at the outbuilding, the earth must be provided by a seperate earth rod, the earth from the existing building should be insulated from the outbuilding, or have I got it totaly wrong?:D
 
How do you determine the area of a buildings equipotential zone, does anyone have an equation?

I don't think there is one?

Basically, if the building to be supplied is not part of the fabric of the building where the supply is coming from, then the earth is not to be imported from the PME and a new earth should be utilised, an earth rod.
 
This suggests that if you run a supply to a detached garage from the house that a spike should be used every time and not the 3rd swa core as the cpc. Also should you use a spike if you are supplying an outside light in your garden.

I think that I may be confusing myself but I have seen the 2 items listed above many times on a TNC-S system.

:confused:
 
just been looking through my course work and found a similar example to the ops question.I hope this helps.If not my lecturers are talking ****e.

bs 7671 542.1.8 -If the protective conductor forms part of a cable, the protective conductor (ie the swa) shall be earthed ONLY at the installationcontaining the associatedprotective device. This by default the HAS to be the main house end, utilising the supply companys earth,but for the supply cable only.

Additionally you would not bond both ends.For this would then connect the outbuilding earthing system to the suppliers earth , which would cause circulating eddy currents in the supply cable swa, causing nuisance tripping of the outbuilding main switch rcd.
 
The reasion i am cocerned with the 2-3 core is i have an ongoing job were i had to put an earth rod down because the TNS systeam had a very poor earth but this instalation has a lamp post feed by a 6mm 3 core cable that i still have to conect up do i use the 6mm core or do iuse the outer sheath and put an other earth rod down for the lamp post ??????? can any one help with this one
 
you can export the tncs earthing system to out buildings if the armoured is big enough.
enquired about this a few months ago with regards 20meter 60amp sub main to 1 bed log cabin.
25mm 3 core was suggested along with a Ze at final CU of 0.35ohm or less.
would of thought 2 core TT would be cheaper!

elfyn
 
Last edited:
One question i have had puzzling me for a while is if you use 2 core swa for a supply to a remote building with extraneous conductive parts and the armour is earthed at the supply end only (remote end made tt) and the cable is damaged towards the remote end ie fork through armour to phase conductor do we need to check the Zs phase to armour to ensure the protection will operate in the required time? long winded I know but do we need to ensure only volt drop and current carrying capacity are adequate for the cable and ignore R2 armour values????
 
You`d always take an R1+R2 at the extremity of a cct anyway - this would be no different...

Reading taken at end of armoured sub-main.

All beyond that is the TT subsystem.

& as stated, you can export the exponential zone, even for a TN-C-S if there are no extraneous-conductive parts at the location (a conventional shed wouldn`t `normally` have any) so perfectly acceptable in my view.

If there are Extraneous parts, bonding back to MET must be in minimum of 10mm, but as you`re `supposed` to aquire the DNOs permission anyway makes it suddenly less attractive.

TT it then...
 
You`d always take an R1+R2 at the extremity of a cct anyway - this would be no different...

Reading taken at end of armoured sub-main.

All beyond that is the TT subsystem.

& as stated, you can export the exponential zone, even for a TN-C-S if there are no extraneous-conductive parts at the location (a conventional shed wouldn`t `normally` have any) so perfectly acceptable in my view.

If there are Extraneous parts, bonding back to MET must be in minimum of 10mm, but as you`re `supposed` to aquire the DNOs permission anyway makes it suddenly less attractive.

TT it then...

I agree with all you say electricAl, however where do you get the DNOs permission bit.
 
The way i see it is if you export a PME earth, if the neutral becomes disconnected or damaged in the supply network, you have lost your earth to the outbuilding, which, if effect, is a higher risk area as it is outside the equipotential zone of the house.
 
That's true for a pme supply in general Jason. This is why the main protective conductor is sized in relation to the size of the neutral conductor with a minimum csa of 10mm.

Just re read your post Jason, the main problem is that if you lose your neutral, any equipotential bonding will carry the full load of the installation, this is why the mimimum csa for main protective bonding conductor is 10mm.
 
Last edited:
"an exposed conductive part connected to one means of earthing must not be simultaneously accessible with an exposed conductive part connected to another means of earthing" quote from wiring matters 2005 article referred to by Lenny- however, can't find this phrase in the 17th- where is it?

I can imagine, but haven't confirmed by testing, that a TT earth electrode installed at a garden shed may be at a different potential than a supply earth TNS at the house, so this sounds like a good idea, but 542.1.8 in the 17th and that section makes no mention of it, just stating that the protective conductor is to be only connected to one earth (and insulated from the other) if it is incapable of carrying the maximum fault current likely to flow.

Is this saying, as it seems to be, that it's ok to connect a TNS supplied earth to a TT earth electrode, so long as you have considered the current that may flow and rated accordingly?
 
That means that a 2 core 10mm swa whos armour is not sufficient sized for use as cpc would need to be 3 core and the third core connected to the insulated armours at the remote end and the MET at the supply end but not the remote installation EMB???? or am i missing something.
 

Reply to SWA 2 core or 3 core? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
530
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
768
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
510
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
774

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock