Discuss Swa as cpc what size ? in the UK Electrical Forum area at ElectriciansForums.net

dnjr

-
Reaction score
56
Dear all
Testing a garage that is fed in 2 core swa using the swa as cpc
Live and neutral are 2.5mm. I know the swa is fine as a cpc but I’m unsure what size to put on certificate for it
Seen a table that says it’s equivalent to 17mm but in the back of my mind I remember you need to divide by 8.8
So which goes on the very. 17mm or 1.93mm
Thanks in advance
Cheets
 
You are correct in saying the csa is 17mm and the 8.8 factor (there are other factors within the same ball park) gives its conductivity in terms of copper. Most people will just note swa in the column as opposed to a csa.
 
You are correct in saying the csa is 17mm and the 8.8 factor (there are other factors within the same ball park) gives its conductivity in terms of copper. Most people will just note swa in the column as opposed to a csa.
Hi westward. Thanks for the reply( prompt as usual). I didn’t think I could put swa in the box of the cert. it’s the Niceic online cert and I think it needs a number so I guess I go with 1.9mm
 
Well the actual csa is 17mm as the other figure is its equivalent to copper in terms of conductivity.
 

Reply to Swa as cpc what size ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
457
Hi all, I’ve been given 3 flats to re wire and i was looking for advice on the correct size Swa to use. There will be 3 meters installed by the...
Replies
12
Views
3K
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
Replies
136
Views
14K
Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...
Replies
15
Views
3K
Hi all, Hope you are all well and all is good! I am installing a sub board being fed by a 80A SP+N Metal Switch Fuse at source, this is feeding...
Replies
9
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock