Good pointIf it's not a cpc then it just requires supplementary bonding to earth
I'm just thinking during the masonry drill attack the armour may be called upon to act as cpc so beef it up ?
Discuss Swa bonding, what method. in the UK Electrical Forum area at ElectriciansForums.net
Good pointIf it's not a cpc then it just requires supplementary bonding to earth
Depends as the steel armour conductivity isn't the same as copper so tho you might use a fly lead of 10mm the armour may not be even that equivalentGood point
I'm just thinking during the masonry drill attack the armour may be called upon to act as cpc so beef it up ?
Reg 543.2.7 rather clouds all this.The banjos don't even need to be linked together if glanded into a bit of steel trunking that's earthed.
What is the jist of it without me getting off me couch and actually reading it?Reg 543.2.7 rather clouds all this.
Na that's if you use conduit say as the cpc and you take a fly lead from the metal back box to the socket as the conduit is the cpc.
Agreed.Depends as the steel armour conductivity isn't the same as copper so tho you might use a fly lead of 10mm the armour may not be even that equivalent
exactly my thoughts or using 2core SWA and the armour as the CPC.Na that's if you use conduit say as the cpc and you take a fly lead from the metal back box to the socket as the conduit is the cpc.
In this case the trunking is not acting as a cpc it mearly becomes an exposed conductive part because the swa is glanded to it.