B

Bonse

Hi guys

I recently installed a submain and fed it with 16mm 2 core SWA XLPE and used the sheath as an earth....

does anyone know the calculation to work out the equivalent conductor size ? i know it works out to be approx 35mm.

Hope that question makes sense.

Darren
 
Bonse iv got a PDF of SWA CPC values in box me your email addy and i ll send it to you :D
The equation is on there as well.
 
Last edited by a moderator:
This link is a paper written by John Peckham, a well respected Chartered Engineer. It will give you a very good basic understanding on the subject.
The tables for both thermoplastic and thermosetting SWA cables will give more realistic results, without the need for any further calculations, that may be required by the other table posted here earlier....

I have personally been using these 2 tables for almost 4 years now, they are good to go... lol!!!

http://www.electriciansforums.net/a...an-we-use-armour-swa-cpc-using-armour-swa.pdf
 
I don’t know if it’s still possible but at one time you could specify high conductivity armour. One armour in say 4 or 5 would be copper. We used these a lot under M&Q regs. The copper would be just a tad bigger that the steel as it would flatten down in the gland. You would only get them if you went over 120mm cable.
I’ll say I’ve never run a separate CPC with a cable but with one proviso, on many large cable trays within a switch room I would run a 1x1/8” copper tape bolted all along the tray, this could be joined on to for any cable or enclosure.

One switch room I modified had two incoming feeds, one @550V via a 0.3” 3c PILCSWA, the other @440V via a 195mm 3+1/2c SWA (high conductivity) both boards shared the same main cable tray, so both linked via the earth tape. I never worried about earth paths in there.
 
Thanks everyone for the replies. ive only just managed to get back to my computer! will have to sort that damn phone out lol
 

Reply to SWA sheath used as main Earth in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

resitting Saturday my am2 4 sections a3/b/d/e swa and sy failed on protective conductors on both swa i under stand thats the earths i...
Replies
1
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
528
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
616
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock