Discuss The Future of Fuse boards...? in the UK Electrical Forum area at ElectriciansForums.net

In the wooden partition.
didn't you see the video? It's to prepare for all the future circuits for your battery banks and electric car charging points! (If you can afford it after spending all your money on the CU) Just feed the cable into the already made hole...
 
didn't you see the video? It's to prepare for all the future circuits for your battery banks and electric car charging points! (If you can afford it after spending all your money on the CU) Just feed the cable into the already made hole...
Except that they probably wouldn't come in from the back.
 
Last edited:
Well it's smaller than the steel knockout and makes it nice and easy to feed the cables into the back of the CU, so what's the point in making the cutout smaller and more fiddly ?
It's into a partition, nothing is going to be easy to get back entry into that CU.
 
Well it's smaller than the steel knockout and makes it nice and easy to feed the cables into the back of the CU, so what's the point in making the cutout smaller and more fiddly ?
Going with that logic, they may as well knock all of them out, that would make it a lot easier.
 
Totally irrelevant. And there is nothing in the Regs about making a CU 'airtight' , if anything that's counter productive as we're told to install in such a way to minimise the build up of heat or words to that effect.
 
Totally irrelevant. And there is nothing in the Regs about making a CU 'airtight' , if anything that's counter productive as we're told to install in such a way to minimise the build up of heat or words to that effect.
As far as is reasonably practicable, to contain any fire within the enclosure or cabinet and to minimise the escape of flames.
 
I can just imagine Delroys face when he turn up to do a Youtuber domestic board change this year only to find some sparky has completely filled it to the brim with builders foam...

NO WAY NO WAY A QUALIFIED ELECTRICIAN DONE THAT I CAN'T SEE IT
 
Imagine telling a customer that they need to spend a load of money on a new metal consumer unit, telling them how much safer it is in a fire and then leaving a dirty great hole in their wall partition.

There is no argument for not sealing it up.
 
Imagine telling a customer that they need to spend a load of money on a new metal consumer unit, telling them how much safer it is in a fire and then leaving a dirty great hole in their wall partition.

There is no argument for not sealing it up.
Here we go again 😀

I tried using that naff grommet strip, including super gluing it, never stays it place, even when carefully inserting a larger cable. Hager bespoke grommet is the same. Manufacturers should come up with something more substantial.
 
Totally irrelevant. And there is nothing in the Regs about making a CU 'airtight' , if anything that's counter productive as we're told to install in such a way to minimise the build up of heat or words to that effect.
I think that most people would know what Brian meant when saying “airtight”.

Also, I don't understand how you can disagree about leaving a dirty, great hole in a wall cavity.

Have a read of section 527.
 
I think that most people would know what Brian meant when saying “airtight”.

Also, I don't understand how you can disagree about leaving a dirty, great hole in a wall cavity.

Have a read of section 527.
Has the penetration breached a fire compartment because if not no further action is required.
 
Has the penetration breached a fire compartment because if not no further action is required.


The metal CU should be treated as a form of fire barrier/containment, that being the whole reason for having metal CUs in the first place.

Cutting a hole that size in a wooden partition and leaving it cannot be said to be the work of a decent electrician.
 
The metal CU should be treated as a form of fire barrier/containment, that being the whole reason for having metal CUs in the first place.

Cutting a hole that size in a wooden partition and leaving it cannot be said to be the work of a decent electrician.
No metal consumer units are not fire barriers because if they were then you would spend a considerable amount of money on them plus their Achilles heel would be cable entries and the protective devices. Metal consumer units are used because the enclosure does not readily combust, no more. You are misinformed.
 
No metal consumer units are not fire barriers because if they were then you would spend a considerable amount of money on them plus their Achilles heel would be cable entries and the protective devices. Metal consumer units are used because the enclosure does not readily combust, no more. You are misinformed.
I said “They should be treated” I didn't say “They are fire barriers”.

Common sense would tell you that cable entries that are sealed are going to act as a barrier.
 
I said “They should be treated” I didn't say “They are fire barriers”.

Common sense would tell you that cable entries that are sealed are going to act as a barrier.
You are giving incorrect information because just by stating this you believe it is a fire barrier. Common sense and fact are not necessarily the same because the size of entry is irrelevant and requires no sealing if it does not breech a fire compartment.
 
You are giving incorrect information because just by stating this you believe it is a fire barrier. Common sense and fact are not necessarily the same because the size of entry is irrelevant and requires no sealing if it does not breech a fire compartment.
. What constitutes a ‘non-combustible enclosure’?

A non-combustible enclosure includes base, cover, door and any components e.g. hinges, covers, screws and catches, necessary to maintain fire containment. See diagram 1. Blanks and devices are contained within the non-combustible enclosure.

3 How is account taken of cable entries into a ‘non-combustible enclosure’ with respect to
containment of internal fire and escape of flames?.

Good workmanship and proper materials must be applied by the installer. The cable installation entry method shall, as far as is reasonably practicable, maintain the fire containment of the enclosure. Account shall be taken of the manufacturers instructions, if any.
 
. What constitutes a ‘non-combustible enclosure’?

A non-combustible enclosure includes base, cover, door and any components e.g. hinges, covers, screws and catches, necessary to maintain fire containment. See diagram 1. Blanks and devices are contained within the non-combustible enclosure.

3 How is account taken of cable entries into a ‘non-combustible enclosure’ with respect to
containment of internal fire and escape of flames?.

Good workmanship and proper materials must be applied by the installer. The cable installation entry method shall, as far as is reasonably practicable, maintain the fire containment of the enclosure. Account shall be taken of the manufacturers instructions, if any.
It's purpose is not to contain a fire it is not a fire barrier. This is a common misconception.
 
Out of interest. Do those who object to holes in the back of a DB insist upon installation of an interconnected smoke detection system, prior to upgrade of any domestic board?

Surely early detection of all types of fire would be of much greater importance than the short term containment of one unlikely source of fire.
 
At no time have I advocated a huge cable entry hole, and assumptions are being made constantly. The vast majority of CUs that I replace are spaced off on small battens to facilitate all cables entering through the rear knockout. So in fact there is no hole going into a cavity at all. But when some people are convinced they're right and no one else knows what they're talking about then it's probably a waste of time posting at all.
 
Out of interest. Do those who object to holes in the back of a DB insist upon installation of an interconnected smoke detection system, prior to upgrade of any domestic board?

Surely early detection of all types of fire would be of much greater importance than the short term containment of one unlikely source of fire.
Regardless of the soundless/ strength of the argument I'm afraid some people argue just for the sake of it.
 
At no time have I advocated a huge cable entry hole, and assumptions are being made constantly. The vast majority of CUs that I replace are spaced off on small battens to facilitate all cables entering through the rear knockout. So in fact there is no hole going into a cavity at all. But when some people are convinced they're right and no one else knows what they're talking about then it's probably a waste of time posting at all.

To my mind this is the ideal method of installation, where practicable. Neat and provides for future repair or addition, without major upheaval.
 
But it isn't a fire barrier and is the partition a fire compartment boundary. Do you want a spade.

The issue is about leaving a massive hole into a wooden partition.

If some are happy to leave an installation like that, then good on them.
 
The metal CU should be treated as a form of fire barrier/containment, that being the whole reason for having metal CUs in the first place.

Cutting a hole that size in a wooden partition and leaving it cannot be said to be the work of a decent electrician.
No. The reason was because many of todays highly qualified dipsticks were incapable of installing non metal CU's correctly, causing an increasing danger of domestic CU fires. (in the London area, at least)
 
The issue is about leaving a massive hole into a wooden partition.

If some are happy to leave an installation like that, then good on them.

The video that sparked this debate was set in a studio as a demonstration of how easily a particular DB could be installed. This was not a wooden partition in someone's home.

If one is to assume the intention was such, then one might wish to consider all possible alternatives - like that posted by @Dave OCD
 
At no time have I advocated a huge cable entry hole, and assumptions are being made constantly. The vast majority of CUs that I replace are spaced off on small battens to facilitate all cables entering through the rear knockout. So in fact there is no hole going into a cavity at all. But when some people are convinced they're right and no one else knows what they're talking about then it's probably a waste of time posting at all.
That is much the preferred way.....and my way, mounted on ply wood with the timber hole filed smooth, smaller than the metal one, negating the need for grommet strip.
 

Reply to The Future of Fuse boards...? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
893
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
792
Two questions: 1. I’ve had a bulb in the hall turn black with some white powdery deposits (see photo), whats caused this, guessing i should get...
Replies
10
Views
477
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
875
Apparently Dimplex only guarantee their heaters if they are permanently wired in to a fused outlet. If the socket is only about 600mm from the...
Replies
5
Views
462

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock