Discuss To Surge protect or not Surge protect that is the Question! in the UK Electrical Forum area at ElectriciansForums.net

spud1

-
Arms
Reaction score
55
Hi,

A wholesaler tried to tell me that Surge protection is now a requirement in DBs under 18th Regs today. Im pretty sure thats rubbish but just wanted to put it out there. I know alots been added on SP in the new Regs but Im pretty sure its still only risk assessment driven and not a requirement in a single dwelling where cost out ways potential loss. They also tried telling me that surge protection from lightning is required, but I'm fairly sure that theres a probability calc for lightning (if anyone can remind me of it that would be great!) that I did on a design course a few years ago that proved that lightning in this country wasn't frequent enough to warrant a 'SP protection needed' outcome of the calc.

Cheers chaps

Spud
 
Hi,

A wholesaler tried to tell me that Surge protection is now a requirement in DBs under 18th Regs today. Im pretty sure thats rubbish but just wanted to put it out there. I know alots been added on SP in the new Regs but Im pretty sure its still only risk assessment driven and not a requirement in a single dwelling where cost out ways potential loss. They also tried telling me that surge protection from lightning is required, but I'm fairly sure that theres a probability calc for lightning (if anyone can remind me of it that would be great!) that I did on a design course a few years ago that proved that lightning in this country wasn't frequent enough to warrant a 'SP protection needed' outcome of the calc.

Cheers chaps

Spud
Trying it on Spud trying to up his profits
 
I believe there is an exemption you can use for single household domestic properties, but that aside you either fit it or carry out a risk assessment and make a decision based on that.
 
443.4 Overvoltage Control

Protection against transient overvoltages shall be provided where the consequence caused by overvoltage could:

(i) result in serious injury to, or loss of, human life, or
(ii) result in interruption of public services and/or damage to cultural heritage, or
(iii) result in interruption of commercial or industrial activity, or
(iv) affect a large number of co-located individuals.

For all other cases, a risk assessment according to Regulation 443.5 shall be performed in order to determine if protection against transient overvoltages is required. If the risk assessment is not performed, the electrical installation shall be provided with protection against transient overvoltages, except for single dwelling units where the total value of the installation and equipment therein does not justify such protection.
 
I believe there is an exemption you can use for single household domestic properties, but that aside you either fit it or carry out a risk assessment and make a decision based on that.
Where Surge protection may not be required
Protection against over voltages of atmospheric origins not required in the following circumstances but the rated withstand voltage of equipment must meet the requirements of Table 443.2 of BS 7671:2018

Where SPD protection is required
Protection against Transient over voltages shall be provided where the consequence caused by over voltage:
a) Results in serious injury to, or loss of life e,g, ( Hospitals , Care homes , home dialysis equipment.
b)results in interruption of public services and/or damage to cultural heritage,e,g (data centers, heritage status buildings like museums and castles)
c) results in interruption of commercial or industrial activity e,g, ( banks, hotels, supermarkets, industrial plants, farms)
d) affect a large number of collocated individuals e,g, ( offices, universities, schools residential tower blocks)

For all other cases than above a risk assessment to determine the Calculated Risk Level CRL shall be conducted to 443.5 (See appendix IET gn 1 for further info)
 
No CRL risk assessment required for single dwellings, just whether it justifies protection for the equipment Thein ie cost.
If the dwelling has say a life saving machine in it like a dialysis machine or other health/life support equipment for treatment at home, then that could come under indent (i) loss of life so it will most likely be required
 
Where Surge protection may not be required
Protection against over voltages of atmospheric origins not required in the following circumstances but the rated withstand voltage of equipment must meet the requirements of Table 443.2 of BS 7671:2018

Where SPD protection is required
Protection against Transient over voltages shall be provided where the consequence caused by over voltage:
a) Results in serious injury to, or loss of life e,g, ( Hospitals , Care homes , home dialysis equipment.
b)results in interruption of public services and/or damage to cultural heritage,e,g (data centers, heritage status buildings like museums and castles)
c) results in interruption of commercial or industrial activity e,g, ( banks, hotels, supermarkets, industrial plants, farms)
d) affect a large number of collocated individuals e,g, ( offices, universities, schools residential tower blocks)

For all other cases than above a risk assessment to determine the Calculated Risk Level CRL shall be conducted to 443.5 (See appendix IET gn 1 for further info)
The missing bit
Where SPD may not be required
For single dwelling units where the total value of the installation therein, does not justify such protection and the consequential losses are tolerable
To be read as "Where SPDs may not be required"
Page 39 18th edition
 
would you like a spud in the consumer Mr customer ,just in case THOR the god of thunder and lightening decides to throw a wobbler out side your house .
As long as it's a roasted Spud, which it would be if it didn't work:tongue:
 
Can't move for the amount of heavy industrial switching in my area causing transient over voltages...

As for indirect lightning strikes, more chance of the house getting hit than any of the distribution network as it's all underground to the transformers, nearest overhead supply is over a mile away but the total distance the surge would have to travel is nearer four miles via a couple of transformers, a power station and all the surge arrestors on the pylons.
 

Reply to To Surge protect or not Surge protect that is the Question! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All. I am taking my 2396 written exam in December this year, therefore i am knee deep in practice papers. In case anyone else is in the...
Replies
8
Views
1K
Hi, I have recently had 18 solar panels (390W) fitted to my roof. The system is a GivEnergy. A Gen 1 Hybrid 5kW inverter (Gen2 version could not...
Replies
6
Views
3K
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
3K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
882

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock