Discuss Tp+n Dis Board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

L

LankyWill

Morning All

I have a Hager TP+N Dis Board that i am installing later on this week. I need to purchase the switch disconnector for the board separately. Im unsure of which type to buy as i am getting conflicting statements.

Its Between:

4 pole 250A Switch Disconnector
3 pole 250A Switch Disconnector.

As its a TP+N board i thought the 4 pole would be better but one of the old boys say if their is a borrowed neutral it could become live!
 
Unless its TT then there isn't really going to be a requirement to install a 4pole incomer. Installing a 4 pole incomer could be a bad move if there were to be a UPS or similar referenced to neutral on the load side of the incomer.
 
Thanks for the help

Its a TNS earthing arrangement, 3 Phase with 400A per Line. This would be fed directly from the panel board on a 160A MCCB. When would you favour the 4 pole switch disconnector?
 
Hi - 537.2.1.1 says not necessary to switch the neutral if it is known to be reliably connected to earth via a suitable low impedance (as should be in your TN-S). In case others read this, for single phase domestic or similar then 537.1.4 applies and says we shall provide an isolation switch for both live conductors. Cheers, David.
 
Hi - 537.2.1.1 says not necessary to switch the neutral if it is known to be reliably connected to earth via a suitable low impedance (as should be in your TN-S). In case others read this, for single phase domestic or similar then 537.1.4 applies and says we shall provide an isolation switch for both live conductors. Cheers, David.

Cheers Wilko thats a good bit of info thier.
 
Hi - 537.2.1.1 says not necessary to switch the neutral if it is known to be reliably connected to earth via a suitable low impedance (as should be in your TN-S). In case others read this, for single phase domestic or similar then 537.1.4 applies and says we shall provide an isolation switch for both live conductors. Cheers, David.
I would keep the N closed too.
 

Reply to Tp+n Dis Board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all.. Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin...
Replies
5
Views
930
What are people fitting in the 3 phase range just lately, I've had a scan at various makes and it seems to be a ---- up between Hager and Wylex at...
Replies
9
Views
840
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
581
Hi all I am new to this forum and hope this is right placed and of interest. I would like to make a setup with one or more impulse relays...
Replies
9
Views
1K
Hello, I am in the process of purchasing a property. I have made an offer, and after my own little survey, I noticed a few issues with the...
Replies
3
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock