Just checking the correct way to do a twin inverter system feeding into Inverter/charger set up. 2 x inverters AC outputs go to separate isolators then each isolator goes to separate MCB's and from there into Henley block to feed into generation meter (for FIT's) then into another Henley block to connect to inverter charger output (from batteries) which feeds building circuits via existing DB with CU. So we are only measuring generated PV from inverters.
So I don't need a garage CU but just a twin MCB enclosure on DIN rail for the inverter supplies.
Can we use these? (image has cartridge fuse holder not MCB).
IMG_2236.jpg
 
Hi Fred, you'll need double pole MCB's for each Inverter, and yes they can fit into a little 2 gang isolator box, (proper sized tails to the henley's)_just remember to make sure the cable entries to the 2 gang boxes are well sealed (monkey poo or similar)

So with all that work (2 x double pole MCB's) it might be easier to run a single pair of tails via a meter into a 4 gang (garage / shower) CU with double pole mains switch and 2 single pole MCB's (I've assumed you've designed out the need for an RCD)
 

Reply to Twin inverters into single generation meter with MCB's in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
675
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
780
Hi all, My 3 month old grid tie inverter has tripped on 3 occasions at startup. Have read plenty of threads here about similar issues but unclear...
Replies
1
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
446

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock