Discuss Underground Cable Route to device which needs TT-ing in the UK Electrical Forum area at ElectriciansForums.net

M

Matt_M

Hi guys,

I have a bit of a quandary about an installation I have coming up; I need to install a 100kW rated Electric Vehicle charging station in the middle of a car park.

The supply (PME) will be in a toilet block building approximately 45m from the final location of the charger. There will be a 125mm duct installed 600mm underground with warning tape 150mm above it. The charger itself will be isolated from the PME supply and earthed to a Mat-lattice.

The charging station itself is metallic framed and the cable entry point is dead centre on the bottom of the unit. There is no way of terminating a SWA and even if i could fabricate a bracket for terminating a SWA into, the PME would be exported due to the metallic case of the charger.

So, my question is, how would you get a supply out there? I have come up with a couple of options and am interested to hear thoughts and suggestions:

1) I run a SWA cable (or dual supplies to reduce cable size) and use heat-shrink at the charger end to terminate the cable (not right keen on terminating a cable like this)
2) I use something like a H07RN cable (i'm not right keen on putting a cable underground without armoured protection) but it will be easier to pull and terminate

Thanks in advance,

Matt
 
Why not terminate into an isolator (locked on of course)

Then from isolator to charging station.

You could then gland from isolator to charging point without connecting the armour from isolator to charging point

Using 3/4/5 core
 
I will be probably be able to use a stuffing gland. The cable size required is 95mm so it wont be right easy.

I guess i could use 2x 25mm SWA and run them through stuffing glands on the bottom of the unit?
 

Reply to Underground Cable Route to device which needs TT-ing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
519
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
737
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
562
I have a customer who is having Pod Point install one of their chargers at a car port, some distance from the house. SWA (10mm2) for the supply...
Replies
5
Views
4K
As the title says, does a three-pin socket (external) used as charging point need an earth electrode or open PEN fault? Are mode 1 and mode 2...
Replies
17
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock