theres nothing wrong with fitting a relay mod in series with a sounder circuit,the loop will still be monitored,or you could fit the eol in the relay if its the last device,many fire manufactures make them for such use.
Yes as i said if its designed for use with F/A systems there isnt a problem and as long as it forms part of the monitored circuit which , ive seen faults arise before where a standard 24v dc relay has spiked the electronic, i wasnt teaching you to suck eggs here as i do see you are well aware and educated in this area but to the newby joe blogs he could mis-interpret what you said. No offense meant :)
 
Yes as i said if its designed for use with F/A systems there isnt a problem and as long as it forms part of the monitored circuit which , ive seen faults arise before where a standard 24v dc relay has spiked the electronic, i wasnt teaching you to suck eggs here as i do see you are well aware and educated in this area but to the newby joe blogs he could mis-interpret what you said. No offense meant :)

non taken mate,i know what you mean about a bog standard relay on the loop,the coil could put a fault on the loop,you could get round that with a couple of diodes but i would never put anything other than a properly defined fire relay on to any loop so yes i do agree with you..:love:
 
Yes quite correct, but that situation applies only to sealed stairways that have been classified as emergency escape routes, and fulfills all the criteria. ie, ...fire rated landing doors, landing doors must open onto the stairwell, doors must not allow substantial air flow past them when closed, all doors to be mechanically held closed (sprung/hydraulic door closers) Stairwell must not contain any flammable material etc etc...


These types of stairwells have a forced air supply to open roof vents, to a give positive air pressure within the stairwell that also helps to keep landing doors closed. All such systems can be over ridden by any fireman's control point...
Yes its all ringing bells (pun intended) also there was restrictions on hallway/stairwell furniture in that pictures etc werent allowed if flammable, but can understand reasons for it.
 
This thread illustrates perfectly the need for a Fire Risk Assessment-anyone here can tell you how to get a Velux to open in fire conditions but to decide whether this is actually needed or indeeed safe is a different kettle of fish and one that requires careful thought!
 
let them fight it out, i was enjoying, your turn alarm man, engineer 54 be ready..... i know its not upto me to decide this decision but i have changed his mind anyway as he already has a remote
 
let them fight it out, i was enjoying, your turn alarm man, engineer 54 be ready..... i know its not upto me to decide this decision but i have changed his mind anyway as he already has a remote

its no fight ip,far from it,good discussion of views imo,personally i like auto venting when it aids smoke ventilation and the escape route for people,as for fire containment and fire fighting it will be a different issue
 
Last edited by a moderator:
let them fight it out, i was enjoying, your turn alarm man, engineer 54 be ready..... i know its not upto me to decide this decision but i have changed his mind anyway as he already has a remote

What the hell are you on about??


im sure in 5 years or so, il be offering him this option for extaÂŁÂŁÂŁÂŁÂŁ and know what is right

It'll be a good deal longer than that i fear...
 
relative to most guys here I know bugger all; i know what I need to, and well, but this discussion really had me interested in the whys and wherefores of smoke venting etc. I've fitted smoke and heat dets before but never thought of it past that.This has been a truly enlightening post. Many thanks to all involved.,
 

Reply to velux window opening when heat detector goes off in the Australia area at ElectriciansForums.net

Similar Threads

I currently have a home with 7 interconnected, hard-wired smoke detectors. I have a hard-wired heat alarm in the garage that I need to have...
Replies
4
Views
2K
Having a bit of a mare at the moment with a small 2 story HMO (6 single rooms with shared kitchen) which was fitted relatively recently (2016 or...
Replies
18
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K
Hi Is this possible. I have wired in smoke detectors in each room in a 4 bed semi. However they are not loud enough and I worry in the event of a...
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock